PDA

View Full Version : oil differential problems







miz
26-04-2019, 04:31 PM
hi all i have a grasso rc 46 compressor from 2003 and it is keep falling out on low oil diff but i have plenty of oilpressure and suction pressure is altso ok and discharge temp is altso ok. but it have some cut out every 14 day

i have changed the oil pressure spring and ball with no result

oil pressure is 7.5 bar when running 50-100 % load and 11 bar under startup unloaded so oil differential ia 3-4 bar under load
discharge temperature is 83 degres when running and suction pressure is 3.8 bar
set point on chiller is -6

and controller on this chiller ia a gea gsc simatic C7-633 controller from 2003 like compressor

and compressor is running with Danfoss hvac drive min drive speed is 900 rpm and max is
1350 rpm. and under startup it is running to max rpm and then going down to 900 rpm

hope anyone can help
15389
15390

cricri
27-04-2019, 07:12 AM
Hi Miz,
oil pressure 4 bar is differential pressure? if it's differential, it's high should be 2.5b at 50C
at hi speed; 1470 tr/mn?
what is your minimum driving speed?
start and stop sequence is set by the GSC?
you mean a GSC TP, with or without a data storage (how old is it)
does it stop during normal operation or start/stop sequence?

miz
27-04-2019, 08:53 AM
hello cricri

start and stop sequence is set by my gsc controller and it has a memory card in the side for the program .

i have added some info in my original post hope it is helpfull too make you understand my problem

cricri
27-04-2019, 11:20 AM
so there is no logged datas on these GSC. min and max speed are OK. what is the oil diff pressure safety setting?

miz
27-04-2019, 04:29 PM
the oil differential setting for low cutout is 1.0 bar and i can not see the high cutout in the controller

cricri
27-04-2019, 06:03 PM
your oil pressure safety trip is too low and the oil pressure during normal operation is too high; but this is not the reason.
suction and discharge oil filters checked or replaced?
is a discharge temperature sensor fitted ?

what can appen to these compressor is a failling capacity control mecanism. then discharge gas and suction are mixed and the discharge and oil temperature rise with a low oil viscosity.
could be screw 14 or piston rings (10;5) on Pg 45 (IMM instruction and maintenance manual).
try a monitoring of oil and discharge temperatures.



http://www.refrigeration-engineer.com/forums/image/png;base64,iVBORw0KGgoAAAANSUhEUgAAAfoAAAIKCAYAAADLb43NAAAgAElEQVR4nOy9wYvcSLb2rX9D69rWzrteaZUbv4vZe OOFXqiNF15c8EJQO8MdMFxBwUDD8BoERX9cGD4jMAwNpkB409AUnzAXzFCIz9xrTKGhMT0mEY1JCvG8C0VIoVBIiszKrJJUzw8C7 CylFFIexRMR50QcB4QQQghZLM59V4AQQgghh4NCTwghhCwYCj0hhBCyYCj0hBBCyIKh0BNCCCELhkJPCCGELBgKPSGEELJgKPSEE ELIgqHQE0IIIQuGQk/InbJBnv6EwHPhOA4c5xni/GavV7hJQxw5DhznCH78Za/nJoTMjwMJ/RpZfApv28amzJG jfEm9OE6jmgIHbh iDdJhsLqJF8Q 0f1d7tly4a1uEIcrA7WKO FmxThkeleVwiiGEm2vu8aEgBAiSI9E FKO4pknV5i3N R1G0bZJCTwhR2b/Qt4Rxu8amzCKsegX6GH700ULs9yX0JYosVkZecxR6WR4jTL/ddy0JviIJHgmBf474erPzmco8xdsogOd4CFO7LjAh5GGyV6Ev8wuctoRxy1HFOsHpiTp63yC//BG K8/1BFH2feQkqtDvKswb5MnL9shrNkL/DHG QZEliNQOl3eGtLjNyJHcmvIK0Uq8H36M/BanakbtFHpCyDD7E/ryM KTYzFaOcFfX7/Y0/Thd2TREyFYjxAkX0eOV4R x2nR8jrGiSvdBmd4HfwwM6EXdVwnCOpOEgXh3lF p6MwxW0siUJPCLFl/yN6/89I8s0e/YRbCr06ajoKke7Umm6QJ3 Gf3qBvCyQht48hb71uRQE5X78GNf5Jc6DlfY7lSiy91qsxApBlCDrzAqskSV/Q gft2MD4ivFzTJ2jFIn/TfrEcfGvp4hvv6C9DyoZmDUkXKRIXkTKjNCLrwg2iJmwfQcXHhBrDyHNbLk7XBcyaBrRbUpw3PyAkRKfEpz390in09/J2DfvyshZA4cLOp b0KvCreNX3MoMO38EvnWA/z5Cr06M9G4PZT7efoSoZyFqX8nQ8BYS8DOcVWLwjek4eNB0bE75jZC/xSvwpNGuKTQF5cIO24kp55xiq7GxH7gObTqOBQT4sILL1FYCX3/c1LjU3YX n3/roSQuTBxod/gOn5eN JukGB0LDYSmOaexLjeSuznJvQrBNEbxK2RrANnFSErAeAGefxMGTGeIlZHuLVAqiNXNTDRxSq6QgkorgEX3umF0ola41P2m/0xOwg98hh 70hTESr1/tRA0fp59KEEznkvkeSyg1mi PRJuY8N8vRXbUS8xlUkOh q 6h36l4VYfVe1NUr7fiUoal749/2/bsSQmbDhIW RHF13oiVbZRymSN9L6c6y25QmpWfX2VuQm8oLaFShV5/FiXWyWlXoAC0XChSJJUYANf/EZe54fexOeaWQt/pANbX7P7WzcqOscBONULex9ll3itwZZ7ird6x6ozYB 5FuVbnXuoZLUWIsa3QH B3JYTMhskKfTuCf4XT5Hr3kYQ6/a81mOPMTejFiD6Oq/I21dwVqtDr96ON9vtKLcbKyLXuVASIWte0OeY2Qm wr9Zov6 MBbFpHc362f4dqTq67xyzi9CPLQntfmc7oT/E70oImQuTFPq2yNuunx9CFett/YxzE/qxOg4JvRr4OFBao0JTgJfuIhk7Zr9CP7wfgyyWMzudgD5HmV1qj/rDWBHCun4WQt/qiPYXdbS/ndAf6nclhMyByQn9/kUeD2xEfxuhV6Z4rfYs0CivkZyO7CJoPEZ5xtrUsira1iN6xce83W89hLq3grimYlftKfee52gxdT8eOyBPJd vbodlcOr UL8rIWSyTEro9yLyRYZEnWIsc1yeKaOSrXcke0hCj1a0uuuf4aIVqJchid8gyf6o/l/mSN bwLRTNsF2xzTGnEqv3vxEZGyvMta6NVgPNdHeJFpS/1i/JR8GpnV2SBP3ylL8UzbOitT7nUchL6jojLitgrGO4YfvlOC 6qRdfxTgkypsNoB0kfZw8F4e/pdCSGz4Z6E3iSeln5EuXxKFTd17fSgf1bz9fedY7SuE2OfQj/qdzYLV7uIZWW2x0BfCqhOJ/8A7wfDbnKDQo9OJ0Ev4 6btrunVepdBtWRsnZvL16IZ2gj9IDRL64W3aVhmu4Xz6d3ed0 f1dCyGxYntAbG/ie5C4U t5jm73UVdH1Eb75uQlGKzIk jF60JbNMdUVUWTvlA1ajuGHMdL899YGP9ZCX90E0revtXwFx/DD/8TbtD KvmKNLIm07 rBeIbjpK9 I38TW6EHqlmEv2urRMTmO4ZAuLLe7MhG6Pf8uxJCZgPT1BJCCCELhkJPCCGELBgKPSGEELJgKPSEEELIgqHQE0IIIQuGQk8IIYQs GAo9IYQQsmAo9IQQQsiCodATQgghC4ZCTwghhCwYCj0hhBCyYCj0hBBCyIKh0BNCCCELhkJPCCGELBgKPSGEELJgKPSEEELIgqHQ E0IIIQuGQk8IIYQsGAo9IYQQsmAo9IQQQsiCodATQgghC4ZCTwghhCwYCj0hhBCyYCj0hBBCyIKh0BNCCCELhkJPCCGELBgKPSGE ELJgKPSEEELIgqHQE0IIIQuGQk8IIYQsGAo9IYQQsmAo9IQQQsiCodATQgghC4ZCTwghhCwYCj0hhBCyYCj0hBBCyIK5tdA7jsPC wsLCwsJyB4VCz8LCwsLCsuBCoWdhYWFhYVlwodCzsLCwsLAsuNy70BNCCCFkv1DoCSGEkAVDoSeEEEIWDIWeEEIIWTAUekIIIWTB UOgJIYSQBUOhJ2SpFBkuQh u48BxT5Gsyzu6cIl1cgrXceAGCdb4iiR4BMd5hCD5uqdz3hPrBIF7i cpv3 rZ0HIdlDoyQxoGvnGXo7hh QFXclXnPjO7LoCRzHxSq6gv1T2iBPf0Ycv7/Fs70jUS5zpG9jxEmG4lDXsKpGirfxWySZxZ1S6Mk9QKEnM0ARetdH OY/EfrHcBwH7kmMa2q9gR1H0eUVopULx3mCKPu 47XvRujLLMLKceCsImT3ZgNbdqgo9OQeoNCTGaAK/SmS9Y0ywn CKPtD/N FF/xFdAKkUK2RJRECz63szAtwnuZNg1zmSOMQvivtUDbAG RpXHconFq0TCKmN/bl7vXp3Hpf/YAyv8CpPI9yrhspgGqpp5r7rm aNXHgrP4PLi8Moi07BO5zxNeb3t/LOHVfi90KQfTXpi7OMfyzvyN5dybud4XT5Fo8G/Wc/w/eBI 0Hb/6hbbMU8TShVE/i98MHSFZz3bnQXYo3CDBWp26/3Ih7kMtTQdJv27r 84x/FcvxX268IK4PYNSZEiiAJ4j//4T0lw 5z7bJMQMhZ7MAFuh18Vhg v4OVznGH70EQXWuIpO4NaNsfz7Y4TpN3GpP1D8UaK8jnHiuvDCSzEtfIOi A7zaLVP6Letj05//YAS6/fnOLsQ09blNZLTlSI0phG9xfVNI3qTX1p8ZhaYEaGvr HA9c9xVcjn3YjWN9lZqa/Zfe5WI/ryM KTYzjeGVIhpGVR4A lM1Z3EJR6Nfcvj9M6KXW9ekb0xSVCz4XjnSLO1o391EKvPxu1HqLO7gmiqzVQfETkH9f32W bhJih0JMZ0D91XzV yt/VRr8edfYJVNPItkdMyvk6I 4thX6r uj01W/oGck6GITe5vrGqXv9XJr4Dfxew0JvqJusfy2IuuBuKfTq7MH5JfLS8DcpoFmElXOMp/6flHsTdZfPzEro5WfHOIk/t2cZOlP38tjufTU2oT7v3wZskxAzFHoyA8zTyq7/Iy7zDczii05D3v2saWTl9K cQi316e96ZLad0G9XH/2 sHGKakW1PYBqG3ub5R6EsU6Rk8Xbh7I89vI/T69P4thb41SheCH1 JkbCs1xNE2TfxrJ/gdfyXRmjl9 U1rIR ID5iQOjbnVb1fO3POq6Z2jYJMUOhJzNAn7rXW/URYdX9zqo4lDnSc kLVYVygzz9SfEfd2cPdhb6ofp0br2nfvXo3MfZZTWqq4TPQugHn0dPMJ46GyB80/1 4QkJPYAyv8R5sDL40VUBfY L4FF1rpvmXi8uXyvPFHco9Kbfacw2 58BedhQ6MkM2FHo9dHYEMUVYiEGbQFbI4tPK6HV4gOa43Q/6x7qM1K/f3VEboupe6sRsB430ExHV1PbQ1H50xJ6Wacii4U4djs/7otXeLVyxbnlvf4Jr8Ln7Xs94NR924VgE8Wv2yaVnpih0JMZsKPQd4LPqs/yNEac/l79 8NH4bdtB76V Ud8ED7xTvCTbKxFgFcTSDYi9KP10emvXyfqXQZsDQm91fUb4fKC16016i13xqC43o3QN99ZIYhi8zr2MseHD3k7yE0JzKs7aT948 FxlRUMWYeUcwfMemV0dih3Wz8ULEMn9BzrBeCII0ELoO8F44j7Sn94iXZfDtkmIAQo9mQG7Cj0A0zRnvSRMWU7liEC/iwxFJyZA35xng/zyx3rJm uH FvoK6PpXeuj01e/6p6bEaoQmSiANyj0dtcv819w1gp2lH/QAuYsfq DCn3rd ipk aucP0zXLQ6BD22pa4MMLlfWsfmuDyTsRLq8jrNZbCKkP3LQujFOdsuG7lnxJhtEtKFQk8IsUQNXuNyLkLmAoWeEGKF3KCHm7MQMi 8o9ISQYerpb8MOboSQyUOhJ4QQQhYMhZ4QQghZMBR6QgghZMFQ6AkhhJAFMymhZ2FhYWFhYTlcodCzsLCwsLAsuFDoWVhYWFhYFl wo9CwsLCwsLAsu9y70hNhAWyG20FYImVgwHiE20FaILbQVQij0ZIbQVogttBVCKPRkhtBWiC20FUIo9GSG0FaILbQVQij0ZIbQVo gtc7eVMr/EebASbeQKwfklciYPJFtCoSezg7ZCbJm1rZSfEZ8cw/HOkBY3KK7O4bvHOIk/Y1etv0lDHDlH8OMvO57hC2L/CM5RiPRmx1PsBVEPP0a 8zlukMfP4DgewrTYY92mB4WezA7aCrFl6rZSCa 1lkITx7Db4mySdxKFNl7vAl9uOo5vDOkRbc7QKF/mFDoyeygrRBbpm4rlfC6WEVX3VH6qNBvkCcv4TkOXP8MF9m6OqzMkb59j4xCTwQUejI7aCvElqnbyqDwjkzdl9cxTlwH7kmMa8u5 fAr9w4RCT2YHbYXYMnVbGRPe/mC878iiJ3CcRwiSr1tez4UX/BmB5zbnja/QeKk3yNOflL8fww/fiRkCg9AXGZIogCfbctdHGKdVPYtLhJ4LZxUhk52RdYLAdeA4TxBl38WHX5EEj3pcDiWK7B1C/1ipz1 q ilC335W2ixHcYVY VtVH4OPvshwobhBXP8VXgcrOM4zxPkNcJMiPFI/d A4LrzTi0kHSVLoyeygrRBbpm4rHR 9F A8zS2C7YQwSgHa9nquj7PLHKWcNag7DCWK9Ayecww/ ogCpZhJcOGFlyh0oZffl fDGll8Cs Rx8sOiRT1EuvkFK77A7wfjhqXxTpB4Pa4MGRnwXuJJN8A5TWSUyGyUujFMa5/jquiBIqPiHw5G/KHqMNjhOk3ABvk2WcUnWC8b0jDx3CcFU6Ta5SKa0QXeqd PmtcRSdwt xw3TUUejI7aCvElqnbSpl/xId8g2rUGotRtBSkIW4n9G6QYC3rkEVY1Z J86ojcCnWRyHSG1XohWjrMQblFaKVW9etOr88pjq/G8S4CD1xHXkedYRfn0z8TRNSOSvgx8hh/n51XQ9h lUI/TH8s1 Ukbcm9OKc6rPpPGcp9O4pknXZen5HYYp79WYMQKEns4O2QmyZl61IwbIRjdtM3WuugjyGX4 OhZB3VgLIUe1/K0IvhVJ3PRRIQ68RUCn8qwjZtwSB whB8psizl8MnQv9PvUOjeqjl/Uw1VnUrcyRngv3gusjvMg6I/pKsPV7kcdoQq 6LsTzo9AfsALk4UFbIbbMy1Z6Rsh9R8tgPDldbcFuI3oVixF9PQqWI2wp1n/Cq/A5XDkaltP1r17hRd 0fS2024/ojdS eg9h q09oheCbTWip9DfbQXIw4O2QmyZuq2U Qe8FwFjZX6BU8 F4z5HfL2x La6vC5EXPv2N8jTXweW1zlw3BNEV vGl127CxQffT3NvUGe/oy3aY5yax 9oA7AU4VUiqgemKc9o7pD8yMuR3304hgAZZ7i7dsUeVmiyH5Fmm A2qf GGH6VfPRi/rU9zLgo6fQ320FyMODtkJsmbqtyNF0Hb0dREiy9fgX1XPkKd6qUe8DwmmMuq nsiUb5GmsRLkrwXvbRt3XSFFXR aNq6J/BqE6rht1/zdEwQ t75V5iri1cZDsrCjXaa0yGI 6d7wXCA1R9xT6O64AeXjQVogttBVyO9RAxPuuy 5Q6MnsoK0QW2grxJ5qO E4kbMbG SXPypLC cLhZ7MDtoKsYW2QuyRwq66QNTNguYLhZ7MDtoKsYW2QgiFnswQ2gqxhbZCCIWezBDayhgPJ8/2GLSVe2YGEekPAQo9mR2zthV9 Y7NJh81G Tpu 7yq4G0pA dWdvK7Oixz7uA78AgFHoyO ZrK3ItsUyaUaLI/su cerkJwc6W3SSFvO1lRlitM 7gO/AGBR6MjtmayuGhBhbQaHfmtnayhyh0E8WCj2ZHbO1lTqrl55FS/5dSbzR2rHMlGjkCP5//HuVjKRVniHOv7d99FY5tNfILs6apUWuj/B1AO9eGu79MT1b6cv1fiO2njVngnNPYlzfaPahL/2SHcmnId6cSfeQCy IlVmjEkWWIGrlbVe3z5WiuUIQvlC2f/1Dq7ea773HPuMvmo9eJLupbUvuPifSz9b1G889XyMT8nTegZuBZ12inl07eoHoZ83uLy6Rxqeifuq7KpP1PEX4RvmOd4r4PtwVW0 ChJ7NjvrYic3vLBkLNPS5yYcs9yFt7couUpdYj huj0Pfn0C5rkZHiX 7TqHfIyO53uW 8fW2rlqK1jJH r7ZqrbaA17pGNS/s/wdlb3wT2Jcl4Z94 skL42ddfbDB9DZP79TV5jt0yT0jkzEc1O/D/X 9za55zuY3oGRZ63UpbmWuCfHEXnsfxf56WUcTfc72 cnuB8o9GR2zN5WWgF5wl8vM3kZRnN1xPJthb43h7ZM5qG6FKTIUOj3x1iudz33unZ8mSONQ21DF0UkTa6hVm74f2pZ5cQhcr99Ia RyP/x2NjnD/veOdi1roVf2u5f1M96/oJWpzoTpHRh71oa61Odp7r2d1tf0HZmZb9rvCYWezI5l2IoccYgGzDgF6bRHMrcV r5EHLKx1RvSe/O57o9p2cpYrvebWtTcIMG61fmTgrJCcH5ZTSXrv5vpd66vqeSS133Z2vcqcWsvzaw6Ay684CeRBc6QJ95a6NVzq0lybHLPmzC9A2 PP puoi m9ae7BLPRq/bvfmSIUejI7FmMrUtxXEbJ/GUb0xuMPIPSyUeSI/sCM5XoHGhfOv H162dKjnVD1jh9pDs0ondPkax/M47o6/OIenWF3rQvg5anHdiD0NvknjdhO6JXKW4h9KYRvVbniUGhJ7NjvrayQZ4mWl5sKe6ygZfpQCHWBv8sjkcz2juJcV2u8Sn7DWUtyM c4iT jLD4jy//YUuibc8jAI/roD8FYrndxlJK6tpO7vRPDYRB6k49enMfeR6 KsWIfLX 30xZKk31uJfTKOYZyzxuea/cd D7yrG8j9CYf/Y4rae4ICj2ZHfO1FTkKkjavTMMCRh9s3eABANbI6mhgZbexurF2RCP6bUuhF dWo 7rqGsK/X4ZyvUuqP3q2iix9TsbotHrEb2PV692jbo3T93rttes4FCF0mCf2wp9J rehRf8uT/q3vhs5PmHnvVthP4Y/quXPVH3pnu8fyj0ZHbQVu6GamQ5rQZrWx6UrRh99AtAD0q9N6Yp4jZQ6MnsoK0cgCJDEjdbiJb5Lzjzj8Uyo lOSY7xoGxlEUK/Rpb8vdlGt8xxeea3l5neGxT6e6sAmRH1SyumhuMr7PK60Fb2Ty3s6rKtekOU fKgbGUJQt9qI5rp9mrjqPuGQn9vFbgbDBGvZHvKHB8 5CixwXX8HO6OASzTthUyJWgrhMxZ6G VBWwEZkI6DK2AGS1idwvYeBNbaCtdqsh7GUG/LKp7m8I0/7SYqdDfMgvYIEyQcBjEelOxVWQVzUqhJ4eFtqIj2k7vDGnxPwObyjiHXVpZLwVsl/6AO9OsarNEtVlZUN2f3PKXVMxT6G bBWz45BT6gyATWpwiWcs9pCn05LDQVtrIHe66GzOZNsU5ILINH9w8SEUXekXkW8mZ5AY2e5zhXQDzFPrBLGBmoe6uDdXXDQ9lA/vvbm yyJBEWqaxOK3rUl1PWesqAtCqGQgzcs3m0/BcCYxSg9b6MkvdoMwvcd5aG6sEUulT5vLlMn5u8/zES e9QBiom1kMZYtSN2E5hh88h7fjy8jGm9hCW1EZEsF7EvqhtfEtVKHvE3l5atNe/Q beQr9YBYwG6ESu5CpIlr huzTuuf7Wm9SZjmqN1 QG0XIzEiGDFDFR0T 8eAsRP0d2SGod4USOz6ZzgvUGZ qjFBlcy3vDGnxh3i5pd9qgzz7jKJ 6fXPbZ6fnoWqxHi2qP3BxpvYQltRkAMk4yh6SOjXyJJI68DHzY6Nu7Cr0K9e4c3rfpEH0GwtbX3u5TNToReYsoDZCJWaOKJz0jGh l9stmjONye9JQW6uIYW1v8fc/Y5NZilZH1NGKg9h lVcV5/9 N7z TZCr15zLFvU0A 5HWy8iS20FQWrdk9vn8QKmbqdKFFkcSX6t9ljoeOj13aJ7KAmqRkZPCxhmeGembfQA hkAbMQqkoE wJNxoS L1tRe42lFO0muGR8aqz7HXR6p/0JJwaCacoc6blwM6hrUo2fbyH0xixZpnrsN96BjTexhbai0Nn2WKWnfdIS3lTsITVrvdQWigtxSMBl4qUf4P3gtmc0O7dyyBiueb IAoUc7C1jtY1ZHm9po hAj nolQHXd2wi9aUQvP tPOGHh765fKK0Orc /jT8/o9DbZObaD2y8iS20FYVdhL5nGtw4KGmdxyaSXkF2KHpH4U0bfPlFJpKpVvB0b4VCrzNToR/KAqbkTg4vtUxLAz76IsP7NO/JBvb/7 yj30Xouz76JrmFMeFE7aNvEqCUeYq3b1Mx1far9qweI0x/7/n8m8XzMwm9XWaufcDGm9hCW1HYZereOKLvG zcvm79A4V2nJTMwiezyLVvhVP3OjMV pEsYFoWJccLcB6HeKoacSdTmGK0nUxI/9gx6n7HEb3/Eq MUfd9maUqYY9bGwg1PrXqpXS08/V9bvP8TEIPWGXm2gNsvIkttBWFnYLxDuSjL3Ok76ULsRt03MWQ5U4OQHSxZzBeh5kK/TLpnw4jKrQVYgttRWXX5XUHiLqvg5ebwUSUDO1nb9owRxX7ZuUVl9d1odBPCAq9HbQVYgttpU015b1kETTFaBEK/YSg0NtBWyG20FZ0RHzSYgPV7i4oeE5Q6MnsoK0QW2grXeSoft8bWU2CdYLAbYKXSQWFnswO2gqxhbZCCIWezBDaCrGFtkIIhZ7ME NoKsYW2QgiFnswQ2gqxhbZCCIWezBDaCrGFtkIIhZ7MDNVeWFhYWFi2Kzu1u/tsuAmxgbZCbKGtEMIRPZkhtBViC22FEAo9mSG0FWILbYUQCj2ZIbQVYgtthRAKPZkhtBViC22FEAo9mSG0FWILbYUQCj2ZIbQVYg tthRAKPZkhtBViC22FEAo9mSG0FZ0b5PEzOI6HMF1c4tFbQVuZFjdpiCPnCH785SDnr1LwHsOPPlql4K2Of4ww/XaQ kwFCj2ZHYu2lTyGL94HN0iw7hzwHVn0RLwzFPYxFm0rh6DIcBH6cB0HjuPCC35Cmm96Dt7gOn4ujhXFCxAlWa/IHlbovyIJHsHxzpAW5VbfcU9iXNt ZYZQ6MnsWLStKELvuKdI1lrrs04QuA6F3pLl2kqB9CxAGKfI9yZQ35CGj E41Qi3Gu06AyK4QZ4mTUeguEIcrOrvmzik0JdZhJXjYhVdwf6RyI7zE0TZ973XaSpQ6MnsWLSt5DF85whPg38zNFol1skpXOcxgu AJhd6C5drKBvnlj/BdB46zQhAlyKxHsT3ITuQqQlYC9Qh5CxEcE/LDCf3ugl3VadsOwryg0JPZsWhbEULvv/kZ0cpVGl2gbnhXf0XyRvXJaz76mxThkQPXf4XXwUq8Xy6804s9jv7mwaJtBQCwRpZECDy3LfjCBsyJTcxCWwmeg6MwxU31ibArG2 EuUWQJomAFx32O No83S9F1Qv LOosOirxVTPdX ZIzwN4dX2P4YfvREdG1mmFIHwhjnmG Pqj4X0ByvwS5/U74MBxfYQXmmtBzqL5MXLLpz43KPRkdizaVvIYvuNiFf0D35JTuMoIpZma/IjreFzoHUcGJa1xFZ3AdR4hSL7e7/3dMYu2lRZrZMnfEPrHO8/07Cb0BdLQU9rxZ4jzm9FrOK6Ps8scZfkZ8ckxHNU2yxzp 0aMKxdCM JuznGC6EpEsYjZCD2upcw/4H0mP5ExBdqoX74vRyHS/qrPGgo9mR2LthUxujgKU9y0Gi8xNemeIllvtCj7HqFXfPxVJ0FtxB8Gi7aVmhJF9h5vRBCd6/ Iyy /3MOI/l3V0Rgd0bcFWdpm/VmZI41D4ZZoivy7capdfW/UWuUp4jq4UBatw2t4X5YGhZ7MjkXbSqvBElP17imSb/9AtHJFY6cvp sRenWE0tMQLp1F2wo2yNO/V9PljgsveI23ab6zn7nbGdxG6NVz9Pu7jT761tS59LWvEJxfVq6m8qqalhdT69U5tFkLk33L73kBzsVzqeqnXZ9CP/79 64AeXgs2la0BqtqmI7x1P TMvVOobdlubYip8xdeEGEJOsuxBxDU6kAACAASURBVNwaGYxX 6q3D8azE/qhEf0XxP5R23a1ehmF3jR137F5GczaI/Scuu///n1XgDw8Fm0reuMkRyWOGg1NobdlubayQZ6 24/A12y5vK7Mkb79uV5eV a/4Mw/HuwYdPzrxUdE/rGyJE/OYkn/u4wvGRF6 Z6owXhS/P1zXBWlcq2hGYVlQqEns2PRttIRZDmVqY6Sbi/0XX/sMlm0rRyCei28acMcOYsg7KwOpFP86P4ZLgY6H8aoez0SvlWHY/jhX6pjh4TeuLyuRJHF7eu8DuBpQs/ldRbfv 8KkIcHbYXYQlt5OOjR XbITjI3zBn8/n1XgDw8aCvEFtrKQ0K4HrYKqpN7U7TX3y8NCj2ZHbQVYgtt5WEhR/VeeGmV1Kby4y9/fwkKPZkdtBViC22FEAo9mSG0FWILbYUQCj2ZIbQVYgtthRAKPZkhtBViC22FEAo9mSG0FWILbYUQCj2ZIbQVYgtthZCJCT0LCwsL CwvL4cq9Cz0hNtBWiC20FUImNqInxAbaCrGFtkIIhZ7MENoKsYW2QgiFnswQ2gqxhbZCCIWezBDaCrGFtkIIhZ7MENoKsYW2QgiF nswQ2gqxZfa2UuZIzwN4jgPHceEFPyHNN/ddKzIzKPRkdtBWiC3ztpUNruPncJ3HCNNvQPERkX8M9yTG9YJzp5P9Q6Ens4O2QmyZt618QewfwfFj5ACAG TxMzjOM8T5zWEueZMiPHKUa04V/dnsgnyeHsLUKnv9bKHQk9lBWyG2TN1WbtIQR53dy6Tw2Ah9iSJ7jzehD1c9h3eGtNhh2P ghP7hQKEns4O2QmyZuq1UQu9iFV2hK8tjU/cb5MlLeI4D1z/DRbauvlbmSN R0ahJwIKPZkdtBViy9RtpRL6I/jxF/MBA8F45XWME9fZr8 eQr9IKPRkdtBWiC1Tt5VRoe/lO7LoCRznEYLk6xbf2yBPf0LguXW725oNkELvvUAYrMQxLrwgVmYIShRZgqj uwPXDxGnOUp8Qxo huM8QZR9r69aZhFWzjFO4s8oO3U4hh G5iBKFFk7xD6x8rxf6m Xwv90DlLFFms/E3OoOg vHrVL X8rnjwHFWOE2uDTMy04FCT2YHbYXYMnVb6fjovQDnaW4hGl RBI92CMzbIE9/bUS1/Iz45BjOKkJWohF65xj 2S/IS k cOAGCdZQZhL8H3GZb4DiCnGwgiNcDNXfVXeEqKt7imR9gyI9g ccw48 okCJ4uocvuvCCy9hDIkrLhF6LhzvJZJ8A5TXSE5FJ8OPkaMcPmd5hWjlNnEL5W/IPq3RCcYbvY7ye7kniK7WtTulurfpSj2FnswO2gqxZeq2UuYf8SHfoD3qFD75QW4j9LEyahVFCpUUelW4pFC6p0jWv4nrmkbsUhB VYS BdYKgFn7xN9mxAFDPThyFSDu3UmKdnMLVZy7WCQJXu17fOTey/j7OLtVOlCr0a4vrNEIvOz3NzMq0I/cp9GR20FaILfOyFSlqDo7CFMPyvdvUfSXIqq9fnkd0GIw euEPd54hzv9b bdSQ/m9oxDpjSrOv4l/y46BPJcpV7qp06LVT6 THyO3OGeZX JcuBoaV4Uq9F8trtMIffP7zGOJHoWezA7aCrFlXrYiBbIvCl87up5CP8eVVYS9SZS0mYEdR/T1yFeOqsU0uPviR7xWXQPG0bdNnbcd0RufWDNrchQivVGfxzeL61Do760C5OFBWyG2TN1WyvwD3otAuDK/wKnnwnGfI7622eZWXV4ng HE56ofvrma6EjovmynK/T1MWtcRSdwncaHPuajr5AjcUcTT8WffvYLcrlMMP0Zb3tiEzrXG/LRG8 5Rvb Q/W59Kl7Z0iLTVukhaj3X4dCf28VIA8P2gqxZeq2Uvu26 j2CImMgLc9R57ibSSX4Mmijbhr1sji0/pY13 F18GqK/StqHs9Kn4o6t5wb51ANUOcQMd/3rpDQzT83xAFPyij KFzylkLGfB4irgzdW KunfhBX82RN1T6O 8AuThQVshttBWyK0QbovxmIlpQ6Ens4O2QmyhrRB71siSvzczKmWOyzO/2ZlwxlDoyeygrRBbaCvEmlrYndb0f3iRmdf3zwgKPZkdtBViC22FEAo9mSG0lTHmESB0F9BWVO5qf3hxHeMGOOQ oNCT2TFrWykyXLRSivZFR5vYIE/fdaOyb5OtbOHM2lb2zvISwZR5irfJ/KfWDw2FnsyO dqKXOYjk2CUKLL/shfoPIbfSYBiylFOJPO1lUOwNKFf2v0cDgo9mR2ztRXTrmPbQKHfmtnaykFYmjAu7X4OB4WezI7Z2orcSrS1g5f6dzX3uBrxa9rL wj f/w7/NZncoez720fvehgNJujiM1ATi UOqyRXZyJXdLEtV8H8HZKoTodJm0rHTeO7KytkSWRlnI1rvPQAwXS0FN I7kRjMi6BsAutStae8BXG990U9b2201f lfNR793 5OdW8325X31vkdyZ8AfEER/057Nz0jTN/W91LvjKc/BeRriTR2Vr6funTYUejI75msr6pajjpaSVOTxlukv661HlTW81iP6G6PQd7c1lVuTyi1Em8a33o6VQn8Y6pSocpc2oMw/4VPxXaSFlZ1BRUxlmlUp9I7c5/6mtqs6q5pFytV6P3q5V35re9hy3G5607 ahX7/9mca0Q /R01aYOk a9LwVlv4/l7Xpc43UNdf1k/ZevgkxvUMtJ5CT2bH7G2lNZITDU4rladA35XrtkKvuAzk9qTVubW0otURYvRDod8/PalXgW5yGADNvvHyt5BCr3xfim4ne1xfgpZSyyonTpNFWNnaTdmX/rVH6PdufwahH3mPvnfSzEK8V8oz1zP4DSX6mYnLjEJPZscybEWOYkSDIhsbU5ENzm2FXl3uJK7XarB1X6fxevNimrbSl3oVjehov 0V7j3Up9OrySVVcbVK79kx/S7dQ/GXcboCe9K89Qr93 zMI/ch79CUNcaSfU3/mfULfWi74xZyud6JQ6MnsWIytqCOJfxlGIsbjDyD0stHiiP6O2HZEr6evHRN6m9Su5hF9Cwuhl/Vrp3/dUuh3tj/LEX3rlm4h9L2pe6c/d0 hJ7NjvrayQZ4mIqiqSf9ZNUrSt6hMg5Y50rc/N0FYMo3mSYzrco1P2W8oldSjJ/FnlMVnZPkfWwq9kr5UBAnSR39gOj76EkX2K9K82MJH3yf0Nqldofjom8CzMk/x9m1aBcmN2k1f tf/2VLod7U/OeX/HPH1dxSfPiEvh9 jWwm9yUevugAmDIWezI752oqWLtNZITi/bCKPyxxpHDbBenr0r5ZitB5V1fnAHdH4f9tS6MW51ahnZ4UgfMGo wNS5ili4 ZJllH3A0Jvl9rVVAdlRcio3fSlf912RA/sZn9a1L88/8B7dLsRvY9Xr3qi7o3T 9OBQk9mB23lbmgFZs0U2sp8mYz9TVzEbaDQk9lBWzkARYYkbrbRLfNfcKYutZoptJWZMGX7o9BT6MkeaKWHXCGIrwb3rqat7J 6YXXU6U5l85SZQluZB5O2Pwr9BITeGAVqC7N8TYIyx4cPebN5xUgkKxtvYgtthZDJCr15jafrh3iz10xFFPpJ0Aomc0bXprLxJrb QVtpU0fhyh7plUt2jsqMkmbrQK9GRRYYkClrbJN4eCv39Izb3cJ8jvpZRsRR6sh9oKyoiSl5dAmfaWMZxcCfLKutla 3SPztrynPfLFNtouCr 5zL9rR3wXyEHgDqfYlHNhaxhkJ//8gEHadI1r9Xa2Ap9GRP0FYaqih2U9u5z3Zwgzz9GbHNzKsU tbmQEPoQq IfGvwJ3cGHNgM6IExM6FHs7uT/LG1jRfM2ZSA7jrNI/jxf4vrHMN/9bK9hlMJCNMzPDXZkNS6ynWfcup5Y5E9aoM8/UlbL/uukxFJrv18Gp4rAStqHfvqcDOcnUqfMl9FyMq Z2hOh1rVTTYQ4kX0XiAM1M05hu z2RzjGH7wHN7IC8rGm9hCW5EMid8 hV503G1Sx rr1UdRhb5P5OWpQxztbUA4f Yn9Poew6Y9kzvZlMRuSao4lr8h /R7EwugZ3kSU8kAUOYf8L6O/pSzCs0LU2dEqjMmwSJ7lNzrXPrLZGYzF1542eoNdzIu1ecSu6GN1MGcneoP8eJLX9YGefYZRe8ztBF6PatWCWxxn9vYDCE20FYE8 r02jp6HhN40QBqa0r8DoV 9wpvX/SIPoDdnwENlmUKvZ1OSW4d2tis07wldTXE1n3V3j3Ja3 n2Hm2yRwl/mSlLlbaM48aQcUlmf5KG3F HvuxUX4XQa7nRezNSbSP06jXt79MWNt7EFtqKoLcNBPqFvm ApJ h6eCbSq/PveOj13aK7PBFiSsYGSgsYEncPpmf0EuxlEuwLLIpVeJm6jT0GLiaPKQe4Ta5w/XztcUO6M9OpSZh DIQDGMSU 2F0Xqs3TpYZKcqc6TnQTXVr7gjzBmpthB6Y5an8fu0hY03sYW2IhhchtzTDg52DvrYYkRfL6uF4kYcEnCZ/OYHeD 47dnLzi0ZEtE8YGYm9E0wXm0MNtmUfh8b0Q8Ifef83axK/SK77YjezNCIXn7WrYNFdipJ/ZK1v9/OSCXvST2f7NAMCb39fdrCxpvYQlsR7CD0/QOkIbYQeh09/qpD46O//CLiehQXa/uWKPQq8xH6enmd6v FZTal37tTUEWG9 kXXI8JvezV6n7uQaGH8r2 7FGK77qeOq8iVt meSuApN9Hr7sPtDoMZqeS2bLUTGqPEaafe55hWUftVp0s6Wt3RoTe/j63sRlCbKCtCHaZuj/0iL6njv2DAnOGvjoOqnVLnLpXmbjQa1O9XoBIplCUWGVTgiGjkYtV9HFc6PVIftdH DpoZVUyimwne5QLL/izIeo Vo5xDL5xZUTvv8QrY9R9Xx2GslPJEb 0mDgGWrZ0xwvwHkc4umg0Nvfpy1svIkttBXBTsF4Bh99keH9jh30bp1ypO/F6iVDgHEXQ4Y OdjQxZ7BeC0mKvQLRbxs227Xa/TRP2AehK2QvUBbkey4vM44QNrTkjXZ VAHcoPr700b5qhi38RRcXldGwr9wVgjS/6ORJlRqBK3bL81I4W zfJshRwK2kpDNdX9EMTPFE/0sKHQH4pWRrZmurrZaMceCn2bxdkKORi0FRUxFb/4ALX9BwDPHQo9mR20FWILbaWNHNXvulnVLFgnCFxtxdMDh0JPZgdthdhCWyGEQk9mCG2F2EJbIYRCT2YIbYXYQlshhEJPZghthdh CWyGEQk9mCG2F2EJbIYRCT2YIbYXYQlshhEJPZkZnW2QWFhYWFuuyU7u7z4abEBtoK8QW2gohHNGTGUJbIbbQVgih0JMZQlshttB WCKHQkxlCWyG20FYIodCTGUJbIbbQVgih0JMZQlshttBWCKHQkxlCWyG20FYIodCTGUJbIbbQVqbBTRriyDmCH385yPmr9LvH8KO PFul3N7iOn8P1zpAWDyNhPYWezI5l2soN8viZeBd6cmmXV4hWbnXMUYj05u5rOTeWaSsHpshwEfpw67b5GH4YI803rcPK/BLnwUppw58gyr4bT3lYof KJHgEZxvhXicI3GOcxJ/xEKSeQk9mxzJtRRV6B26QYN36e4l1cto0vhR6K5ZpK2OUKLL3eBMGOEvHx7fdr dI3/4shL1EcXUO33XgrCJkUhWLS4SeC8c7RZytAWyQp78i6xHaQwp9mUVYOS5W0ZW9aMtOs3pPC4ZCT2bHMm1FCv0TBMFjw hIjFpW/4bg6RGF3pJl2kofJYosQSRG2a7/Iy61UfhuFEhDD47zDHF A A7suhJ/8yTgcMJvaxL/2yCGXlP235vnlDoyexYpq1IoX GN8lfuyOUdYLAdbGKfsYbXxX6DfL0JwSe28wG Ge4yNYA1riKTuA6zRRl5ct04Z1eIH8gI5nls0Ge/l0IvAsviJBkYj7oJkV41LfvuaXwlp8RnxzDcU RrEvUnc76/ NUQu/CC/6s2OoKQXxV 9Q7rgDXR3iRib9/QewfwfFeIJTH DHynpH58LmA5n07XNzAlKDQk9mxTFtpRvRR9kWM3mXjpY5asqrBawm9MmUqG2X5Xfl/5zHC5Gcx3fqwgpCWjRyZmv3ot6dEkZ7BU91JUlzdpwheSDE9hn/2S2/nsRL6SnDPLnOUtV02swJl/gHvZQdFBszVI255nw5c/xxX0n7XCQK36 oaPle7TkdhiqVPjlHoyexYpq1IofcQpmvhjxeNoGhYq8bsi0HoY4T cXu0po62pD/VceC4zxFf71sMpssybUVlg/zyx8qH7voI47Qttrcc0Zf5BU49F473EonsRNTndOGFlyjwDWn4GM6An1yKqirIlW 9 azMU8StIEA1MLVnqj2P4RvEevhc/XVaKhR6MjuWaSuq0Betkcq3LMKqbqTaQi8DkbzgJzGak6N/6U F8pkD9yTG9cMYzANYqq0YKHOkcVgJvrNCECW9gXH2pxQi754gulKlUNigamNCcB0/Rm44l9FHr35HzhJ4Ac7TvHIzZRFW9XeE0OuxKSahHz2XWicKvdX377sC5OGxTFvRhF6Ks/sn E9V/6gq9Pp3gNp/WjfCcur1GH7wHJ7zcJYUAUu1lSHWyJJI MFVu9iOfpEHjKNrK6EfGNF3BFuuMhkRetPU/ei52nXi1L3F9 7AuThsUxb6Yq2bAjbU6Kq0MsGTG4UoiyFkkIvpu2rkbyYYn1A0/fLtBUb1siSdzv57I3T9foxcibp9AK5tKuBTmTjoxcdh IjIl/EjqTfGsGW/vf67yNCbwrGGz0XwGC8Lb9/3xUgD49l2ophdF5vkKP6JXUf/RpZfAqvjrh/hdfBqhL67CPiYNUW9nr980sk e9iZLb7yG/qLNNWDkstyoM fSU2wBjVbjqnFnXf k6JIovbf3sdwBsTeuPyurFzAVxet X377sC5OFBWyG20FaWj1wyutWGObLDzA1z7L5/3xUgDw/aCrGFtvIQkC4p 3X9zb4U23QO5guFnswO2gqxhbbyMKg3ggovLZLaiNiWbToGM4dCT2YHbYXYQlshhEJPZghthdhCWyGEQk9mCG2F2EJbIYRCT2YIb YXYQlshhEJPZghthdhCWyGEQk9mCG2F2EJbIWRiQs/CwsLCwsJyuHLvQk IDbQVYgtthZCJjegJsYG2QmyhrRBCoSczhLZCbKGtEEKhJzOEtkJsoa0QQqEnM4S2QmyhrRBCoSczhLZCbKGtEEKhJzOEtkJsoa0 QQqEnM4S2QmyhrRBCoR/lJg1x5BzBj79s98U8hu84OApT3Oy/VsjjZ3AcD2E6nn35oLTu8wti/wjOUYh0/zddM1VbIdODtkLIQxD6PIa/i1ALdhb6fVLmSN R1aU91cHKyj0ZFrQVgih0I9y/0IvR /PEOcHVM 9QKEn04K2QgiFfhQK/TZQ6Mm0oK0Q8tCF3vS3mxThUeNbr4TehRf8GYHnirquEMRXqLzjUohXCMIX8BynEuX/72 aj75Ekb1D6B839 zHyLFBnv6knNuB65/hIlvX/u92UoJniPPvBh/9GlkSKec5hh/GSPNN675c/xVeBytxjAvv9AL5kEegyJBEgbgvB47rI4zT5jv00ZMJQ1shhEJvKfSVwJ1d5ijLz4hPjuE4jxAkX8VX5DEniK7WyrnleUoU6Rk8x 4UXxMLXvkGefUaBDfL018b/Ls /ipCVgHlErwfjbXAdP4frHMM/ wV5WaLI4kr0vTOkRVnfl Mcw48 osAaV9EJXOU Osi6yHvHGll8Wt1HeFl1dCj0ZMLQVgih0FsLvRskEBKOMouwUj6To/5VdIWydW55nq9Igkdw3FMka334vEGexu2RvuMox1oI/TpB4DpK5wAAviOLnsCR9yeFXqmDvA/zyoAS6 QUrn5f5RWildvUh0JPJgxthRAKvaXQa8fIKXU/Rl4foy11UwVQiqM4XqUSWxde8JOYZpcCLYXdQui1 jS3UnVSjsIUN1LoVREeXAIor6E/uwJp6HWuTaG/Tya03HJi0FbmjGxr5hCfNG0o9NqIVR/l2o/oB4S d0RvaqDFsdsIvXFEr43Itxb6nhF9Xb8niLLvFPp9o8RlqDbXIDuCDoXdgkXbykQo819w5h PCLJoGzoxR87A9yj0 JhC70caUs/dvERkZhC7/rohf 9PuYxwvQbABuhN/no18jep7i6OK1869FHFChRXJ3Dd1Xjl4J7jJP4M8riM7L8j9199NZCD/ro7wM1ANPk6pGdOgq9FYu2lS24SX/EMzU4dy9skF/ KNqrIcHuQba/rQGKCoV XzwQoTf0Iv0YORRBlNH05/ J8OnRcNS96yO8yCCb2HGhB4y FWErJTiKSPuZVS8YtzFFeI6Ut5DmH7bOep K6EHGHV/14iO6dPg37DqzKbITt9jBMETCr0Fi7aVLWhG3S68IEKSdeeKdjgp0vOXCM7eI32z7RJgacsDwcAU r2xfKEni2PRtiJnoN78bBjtCLfJ6q9I3qgdPc2Vs tSygWyaFvZmhJFliAKVprgS0E1Tat3Y3 67LDXhxzNGwOUJbJe6tJlB453irjuqAwsTwZq92wzULvnXU7vCQo9mR2LtpU6buQf JacwpWxEGgCN1fRR1zH40K/1VLKhbJoW9mZEkX2Hm9CH 7YjJ4V2wt9Y8vqjJVO0wFx/R9xmW9QXsc4cVW31sjy5M678DCh0JPZsWhbUV0hwh9fBeWJIDz3FMl6o7lueoTeeinlclm0rexKkSF5E1a ddfH2WWGyzsd0cvg5OeIr4diBqTQqx1UGYwqPxtZnizfhd44gIcBhZ7MjkXbSt9qjW//QLRyhejrqzV6hH7beIwFsmhb2ZIyT/FWxtt4AaK36Z5cOdsJvRyVm1eVqJh89O1lv6PLk7Xl0g8VCv0caK0cMC3J2yBPXgofVvN5mV/gVPiulmToi7YVTZCrhuwYT/0/KVPvFHpbFm0rW1CvHvICREm25ynsbYReCnGzaqmfsRH9P8eXJ1PoAVDo58FYYp51gsBVlrwBqA1eLq9bEIu2FV2Q650IHcO2yBT6 MRZtK1tQ5ine7l3gJVsIfXGJ0BtaUtc6WPHRn OquGmWH3tnSIubeulx7/JkCj0ACv08GBH6qreuBVrJyOvR6bH5sWhb6QiyHMGogUt7EHrTMQtk0bYyGcxC39qZE4C638dJ/HkgCE9ijrpvRdVjZHkyhR4AhX4eWAm9tqZ6wQZOWyG20FYImbzQyx7dU4RvzpodmFrrKMUmLd4LhHLNsDH96zH88J1YhqFvlCNHS 3eYb3Nq7xGK/pU1E2OiPrWa5Y50nNtw5mLoSm0NbIL5V5dH HrAJ7JRx9H5s2ADKUS/KFn0pNuN78ZvgfbNdtFhguxnMexPfeAzRBiA22FkNkIvQPHe4kk3zQBZvXSDN2PI4Q8PYPX8d0IP7a 9W35G7JP6yaCU/i6y/wTPhUlrITeuF7zG9LwsZK Vq5n7gtEUbbKFULZBNT1B PZjehHngnQ3e7X5h5s1mxLv5zSQaue7e9bPp/GZgixgbZCyGyE3hR1KYVPHtNsLNLsIGZI23oUIt3IXZnkHu4VdbIasTlDwxZCr15TBMmZ0ryap9RNyW/kVpG3FfqRZ3LTk2537B5G12wPbHW59fOpYONNbKGtEDIboVdFTE fqgkuAJtMSWV iXMx1dwEd6hT2 q0tr3QtwSqb5/92r2g0ZfOdmR5nZ3Qjz ToT37e 9hNPBLT7ur39cWz0fAxpvYQlshZDZCP7QzkknoTaNXE4qvvvX9xlffStaink K8pDQm0asg4jr3NmIvo3xPGP3MCr0W47oLWDjTWyhrRAyG6E3 eilGJqEXvFHn/0igsI2yNOf8TYV6Vbff6g l2lnvTOk/7zC zRH2fFf65s8SF yMyz0tX9bcRGUOdK3P/eki9TTzR7IR298Jj3nGbsHm6VcHR99iSL7FWn 25bPp7EZQmygrRAyG6E/hv/qZU/UvUnoAeMeyLWgyN2TtPO1cn2rueOhpYqtMj/F4dMRoUclXHGo5Gw2xQCoGKLuf44QHMmR765CP/ZM oR 5B4sN2cp8xRxK pexFRs/XzYeBN7aCuEzEbomXebNLDxJrbQVgih0JMZwsab2EJbIYRCT2YIG29iC22FkMkLPSFdaCvEFtoKIRR6MkNoK8QW2gohFHoyQ2grx BbaCiEUejJDaCvEFtoKIRMTehYWFhYWFpbDFQo9CwsLCwvLgguFnoWFhYWFZcGFQs/CwsLCwrLgci9CTwghhJDpQqEnhBBCFgyFnhBCCFkwFHpCCCFkwVDoCSGEkAVDoSeEEEIWDIWeEEIIWTAUekIIIWTBPAihv0lDHDk ewrS476poFEhDD44fI5f/PgqR3mxzjhvk8TM4k7y/qbHrMyZzpXr3nyHOp/CDf0HsH4n3nZC7Y0JCv0Z2cQbfFTsAuadI1qXd99JPKEY/uyvEy1zvZHQM/ wX5MZbUYV V Yo9LLOzW5Prv8jLvPN/i9VfEKarfd/XjIL oV gzz9CYHnCht04QU/Ie3Y4Hdk0ZPqmN73dIM8eQmvPk MrDC98AcQ psU4dFQ3QiZkNCXWYSV48ILL1GgRPHpU484qpiEch/ieRvEy3wUIr3Z4Dp DtdxsYqu0L2dhy70VZ3L6xgnrgNnFSGz6dtZXyZFeHQEP/6yx5OSOdEv9CWK7D3epjlKlCiyGIHnwg0SqN3CyjYfwfP6BVptu9bXMU5c2Y7pHE7oj8IUU5izINNkMkJfvZDbNspTF3oAeQzf6X sRKfRVnbVntrfLUOgfOvZT9wa3TvkZ8ckx3JMIb171vadyxP8EUfYdwFckwaMeW6bQk/thj0K/RhafiumrHaZi1wkC14Hj ji7zJXRtcUG8QAAIABJREFUb4kie4fQP1am2GJk2f8Lv7XZ/xH8//j37mfxFyG2QlTyGL7jwnvxonYTuP45ruRUW5nj8syH6zhwnBWC8AU8OfLML3BaT/X1CatpRH Mk/gzSs094fov8co/Fi ED/xvWYq0FEaDX260UOYfhOieYyn/p aesdXzYiiuEIcrAyuhC I/WPlWTxDnP B/PJH8X8XXvBnBJ7bNCRFhotQPh8HjneKeOupcfOI3j2JcX1zjeR0Vf G1XUNHSL1N 08l0fw/f lJYN4hjj/rjxjoOsu8hFeZOK5id/Re45A2p57gujKdK/Vsa7/Cq9bz/nvSN6Id6L13WYEKa97dpmjLC4RtkaVJdbJKVz3OeJr7V0as2Pj7/QvFOkZPOcRguSrOFElTO5JjOtSex6qHeUxfGeFF8HT6pwdsep5T4vvwp7kKHeNq gErnweZY70PNBsve9c5cB1DH9zfbx65cO1EXrDsy/SM3juc8TXvw90yPUOghR 0zWlTb1AKO2k1d712EX9Xf1dvanPSaEnQ xX6KVffJ0gcPumq/tQX1Ll5S0uEXqP4Ecfq3MXHxH5j8S5LUf0qijUHYrniK /aw2faFid4 p6okdfCdI/q/N6Z0iLEig IzN2ZHQf/QrB SXyUjQc8tzYNIKqC/33FOFR141RTREqQl18Rpb/IUTThXd6gfxG1FmNcaj91PL 5OhD1nWF0 S6 q3E86lE47voqEjB/YY0fKwIimi0t55y1330jX 0GoE9Rph A7DGp w38 s/Kbm57IxjOjbnSnZCat D3EvdadMjMzk/ztCYPrNm99WPjfXP8fV h IVq5S/xJF9l9CnMR1VhGyUohE/dsJETZdc9COB34nYR/1OdcJAvcRguQ3IWyyQ1KiuDqH7wpbETNTjvcSicnuB99T5VkHz HV9ibvVwqasPX1wLmGriN/I3HfZf4LzvzjHtFVqZ6XU9udvJ8j8Q4OzbzpI3hp2wNCL22q1N/VPrtQv6u8q8o5KfRkiP0JvT6C6J2uHkM2uFVHYZOGODKl61Mj1bcRen2qq9UpEd9VRLKJ2F Lhu8YfhgbgnYkfdPQeiMO1C9zZ0QvRz0 wjgVo2/T94HuNLje0OgjIHU2QoxEFSGp7lcZ8anPSwb dH4PvVHTOjudBnLA3VB8ROQfw/VDxKkczQz9pl97ngtGhN7wO7UCm/SRmt7wjvzmYsRd2ZX d33krMzarBMErhCCWoS/6hcctuPB32mjdPb EDMGp0jW6 p O99RZ8V66lLbTd97CjRiqvivyytEq27naehcXwb dp1FWLXqKDu2Q0IvZ89kB0 pq zUDwq93mZYjOhrO5D1k3UesAvDu6qek0JPhtiT0EvjFr1N8QLvbHyKX3vTeXlV9iD0rf8PCb0QpCJDEgXKqESnT hNS7v6hB6oBDpBFKzEKGq9m9CL30KOxKrRb1vo1d9pUOh7GubtGYsrWCNLIgTeUTVLUYpnp4hscx97FHr5rIxCP7Q0z B7zWP4dcxJ 1p18NbpBXI5iu90KP6C HXPfdX31mPHY7 T7BS8/hter Sota8jqd5PfxxIOfieQnTgfoDnPWpmGnrqOXSuob91l9GOCX0j8vUMAYDurJxJeOurClvewkffEXp1ZqrPLvoEnUJPxtmz0FejhG oaccsRfZnjw4dcmeYTL7NsDGqf/wZ5 g5Jtkbd NY9b5g/sxb6Zuq mlqT/mIPYfo78g8fxdSwxTRu50XfYup I59F2ZqS7U5Rf0Ka/W4n9KsIWSlHVf1CX0/dn8S4LptYgeoYfaoVKPMUb5MM24UB9gt9mX/Eh3yDelTlniJZb6rja7 u ruYpu6Fq JGdYEo1 2Zuq9iTOTI7vBCr043dxt/4XfvE tBOx77nZQlY7VAGVxDZY707ftqKnlE6IffU2WEnP qTIkbpu6z/0ImXB3Gcw1dZ6upezlz2NdhVxkOmpXP7ST jBubqPt6QNSeuh 2Cwo62Z29Td03L5UD13 BF57bFrCxqHDpc2z5teW5L3EeNAFaTQCY9COqrgLDZ9ZCDy0YT/oUK6GXftfhYMOhCHI9YFEEb60iZKUq9DI2QAZ1yeC5btBZkPxzZOpe6VDU99MWoHbjoR7f/Jbq82kFT mBf1YMCL1caqcHI kBha9ewq ntU3PpZoKrRpz6a74tkUw3uGEvmVj7lMEL1ZtMZKNvCLC3Uc4bsdDv1MlKo7mijCtLY/thB597 kXYfPS/y07r1LstHpK0et950faAy2YLXwdwDM x75Ru6lToAl9ZyWN l5brKNvBXgqNj5oFz1Cz3X0xILJLK bKtPdVe O4PKde6DrqiCEkF2h0Ouo05Vyith6l74loE65yqn7Ad8r2TvVMs5HSnAYIYTsDoVeR0R911N5nXX9S0ed7tZdB SwiJF8HZB13/UhhCwBCj0hhBCyYCj0hBBCyIKh0BNCCCELhkJPCCGELBgKPSGEELJgKPSEEELIgqHQE0IIIQuGQk8IIYQsGAo9IYQQsmAo9IQQQs iCodATQgghC4ZCTwghhCwYCj0hhBCyYCj0hBBCyIKh0BNCCCELhkJPCCGELBgKPSGEELJgKPSEEELIgqHQE0IIIQuGQk8IIYQsGA o9IYQQsmAo9IQQQsiCodATQgghC4ZCTwghhCwYCj0hhBCyYG4t9I7jsLCwsLCwsNxBodCzsLCwsLAsuFDoWVhYWFhYFlzuXegJIY QQsl8o9IQQQsiCodATQgghC4ZCTwghhCwYCj0hhBCyYCj0hBBCyIKh0BNCCCELhkJPyE6UWCencB0HbpBg3fk/mQ5fkQSP4DiPECRf77syhNw5FHpCdIoMSRTAq23ThRdESLIh abQT5cdhL7Mkb6NEScZisNWjpCDQ6EnRKHML3DquXCcFU6Ta5Q9nxm SaGfLNsLfZlFWDkOnFWEzPyDEzIbKPSE1EhBcOGFl8pIrkSRnlUjfPcUybrE9lP3zd8dL8Dr0K/ 7awQxFfiWvIYF17wF4T MRznCaLsO4A1siRC4LnV IFOE/zptNR5kjjEL4r3ycpahvkaSzOVf2tv77fkUVP4DguVtEVytvUx3jvu5ynRHF1Xt X67/EK/9YqaNBxMsrRCtXuUb3mKbz5mjXlceq24bKa6Gq78VZ85xdH GFMupfJwhc9TdWv0vI/UChJ0QiG2nTyK8WD10EdxB65xgn8WeU5WfEJ8dwnMcI02/aMerswQbX8XO4zjH86CMKrHEVncCthUz XZ4HQPkHij9KlNcxTly143KDovgO8wxEn9BvW5 he9/yPPI3cZ8jvv7edLhuJfQl1u/PcSYFurxGcrpSju8b0X9DGj6GU9e3 f9J/Lm6p9qGXHinF8ip8GQCUOgJEdSNu0mwavHoE/YthL6eFZDC2j1HS2DktevvoRaU6nvKTETwE9J8072mYaS8ldBvVZ Be9/qPIY6djpcu43ozfVrRt9Goa87Hd361p/VQt/X6SHk7qHQEyK4e6HXBbDnHFI8TKKzipCVTYehCR6MkRWlck9yivoUcbbGtkK/XX36733X 2q 13Rqbjd1nyKu3SfdKfqu0Pd0VnRhN3UGCLlnKPSESO5q6n5XoXcMRYpOmSM9b68UqOq5QZ7 1PjAB6 1pdAP1afn3rc7z4GEvp5J8HF2mSvCfhuhF em0JMJQqEnpKYvGE9p N3niK83uFUwnsXUfescUphsIsCLK8TBShNHAFgji0 VgMIbw7V0Ed1DfbR73 48BnG1mbrvTJ 3j kX8T1O3VPoyYSg0BOiYF5e9wvO/GMtkGwPwXjFJULPNQbjtc hB61Vn VpjDj9vfr3h48i8KsdmFfmH/FB Ow7gXl1hPgZ0kIG7jnjQj9an/573/o8o8F4SkR/eImiPme/0DcjetFpKz4iakXyQ lQrBBEsdhDYYtgPAo9mRAUekJ0rDbMuc2I3serV0PL60znMEzB17ML2pKwesmX2rmoOhh A5ZUTbnvPxRWboW4m tJWG71qf/3rc/j1pHF17wV0TBShPlHJdnft2J8sNIW8LXjbovsri1pC KAnitpXDt6269vI5CTyYEhZ6QO8E0dU 2h9vZErItFHpC7gQK/W78jjSOxZJBZfMc4W4ghIxDoSfkTqDQ74bqc5fT9 peAYSQMSj0hBBCyIKh0BNCCCELhkJPCCGELBgKPSGEELJgJiX0LCwsLCwsLIcrFHoWFhYWFpYFFwo9CwsLCwvLgsu9Cz0hJmgbpA/aBiHjUOjJ5KFtkD5oG4SMQ6Enk4e2QfqgbRAyDoWeTB7aBumDtkHIOBR6MnloG6QP2gYh41DoyeShbZA aBuEjEOhJ5OHtkH6oG0QMg6FvoebNMSRcwQ//rLdF/MYvuPgKExxs/9aIY fwXE8hGmx97NvRes vyD2j AchUj3f9OTsw0yHWgbhIyzXKHPY/i7CLVgZ6HfJ2WO9O17ZMXUc5dT6Mn9QNsgZBwKfQ/3L/Ry9P4McX4A9dwrFHpyP9A2CBmHQt8DhX4bKPTkfqBtEDLOwxR6099uUoRHjW 9EnoXXvBnBJ4r6rhCEF h8o4LcfNeIAxW1d/9GHnHR79GdnEG35X3Ka 7QZ7 pJzbgeuf4SJb1/7v9h7FzxDn3w0 jWyJFLOcww/jJHmm9Z9uf4rvJb1dFx4pxfIhzwCRYYkCuDJ67s wjhtvkMfPZkAtA1CxqHQS4xCXwnc2WWOsvyM OQYjvMIQfIVQIE09IRAn NK tFbAvgNafi43UEof0P2aY1K6H9t/O/y/KsIWQmYR/R6MN4G1/FzuM4x/LNfkJcliiyuRN87Q1qU9X05zjH86CMKrHEVncCt78OArIu8d6yRxafwHBdeeFndB4WeTADaBiHjUOglPULvBgnW4pAyi7CqP5NC/wRR9l07tzjPOkHgts/RsEGexgj94/bI3T1Fsi5hJfTi/E3nAAC I4ueNDMHUujr8zb3YV4ZUGKdnMJ1XKyiK9SnLa8QrdymPhR6MgFoG4SMQ6GXGIVeO0ZOqfsxcin0urgpArjJIqx66lCJrQsv ElMs0uBlsJuIfSt qi3UnVSjsIUN1Lo1XoOLgGU19DrLTs27WtT6Ml9QtsgZJwHLPTtEas yrUe0Q8Iff I3rQe/iuS4NF2Qm8c0Wsj8q2FvmdEX9dPzGBQ6CfAYZ/7HKBtTBjZ9mgDEXL3PEyhl9PQ0o9dfEQkptC7PvoTRFdr5ZjHCNNvgI3Qm3z0RYb36TX lZxWvvXoIwqUKK7ORcCeFHYpuMc4iT jLD4jy//Y3UdvLfSgj/7WlCiyd223TKszNsYGefoOSdbuHpZ5irdJhnveKmlSzM82poIeJOzA9UPEaY5 M9W 4wU4HzqeQj8ZFi70euS6NDpFEGU0/fl/Inx6NBx17/oIL2RDayP0qDa9iUPlhZIjZSme8iWTUfHKCL64QlxHynsI0287R91vJfQAo 5vg5xp8V4iyTcA1sjST/YCbeykimfMRrPF7GxjMmyQpz/jrRTqeiCjxRzVlCjSs6azXw8GniO 3pgvQaGfDMsVerIY5mYbJrfPVlDorZmbbUyZ4b1DNNddr4uvdUIK/USg0JPJMzfbkLEcjetDPyBHeq7NllxkKKSYm2aijDNT2kyK1Z4J2vSr6yN8HcC77 2ed2RutjFdpBuwZ9ntwMxgr5DL76h7jTguvCBWlhVr74JzDD981/xdxFM1M6vztNP7hkJPJs/8bEPuVSAbtp8aV4qM25CxH/WxMvYDW4zozULfv2eCMv0qxL/ML3A64wZ0frYxUYpLhJ7bWobb4jZCX8cQyc6EMttV5kjfN3En5XWME1eZJejYNNkFCj2ZPPO0DS0gT/rr1wkC17xHQR0zcVuh790zQUy/thpzOQVLoX wlNdITldwnBVOk vhafhdhF61NxkILT/rxDCJmCXZEZDn2CqYlehQ6MnkmbdtyJUXQkj7gkTVBvO2Qt8XeCkbWb1hvmVeiPtk3rYxAWqRHxkxS9vZRehNNus8Q5wXYu QFYLzy8q9pNuotr8J2Q0KPZk887YNufeBGMWbRvQ6hxJ6eTxH9ASwF3kA3X0 tgjG6x3R/093tY5csUKh3ysUejJ5ZmcbZY7072IpYmfZkvTRK4F6ZY707c NH19utHQS47pc41P2G8p62v054uvvKD59Ql5uK/TN3gyVz5Q geLzXR9 wu7L6/rxIzI/TikTevxKhT6fUOhJ5NndrYhRyXStvWNRQx Sdf/EZd1wF57jwUp0q29H45CpDfbCr04d2ujlBWC8AWj7h8atQj3uZC0La8B6HZpvWFOK pei6pv7RVyDD/8S2XjFPq9QqG3Qhr9U4Rv1J2hThHXu5f1pK3tpKNVDV3fuMe8mU4zGjRN32ob9/QtR ld0jV9pm0b86cK2FMb9PlA2yBkHAq9FU1KWhk9XU951lNXprS1crpL3 pWTn9pW/GKFLZ1whux3WyZf8KnooSV0BuXo1gs6Zow07aNmVFkSOL39YiqzH/BmX/c2ODMoG0QMg6F3gop4upmElo6WGPaWuGDMqWRPQqRbmRgSntjlTp5Tms6F9hK6NVr2izpmjDTto15UQu7upTJP8NFttMefvcObYO QcSj0Vpj8VXo6V9Pe90M7nVXRq2V iXMx1d80uOp0vzrVby/0LQG3WdI1YaZtG Q oW3MCc2NOebjJ3uDQm/F0IhefmYSetOI3oTiq299v/HVt5ZHqefT17eahN5mSdeEmbZtkPtkN9sQO7TVrqzDM7yP/MNA7npXuSSF 3Aoan8f3GHyrUNTPb/d3K0UeiuGfPRyjahJ6BUfvVjO1M4atUb2/kN7GZZ3hvSfV3if5ih1n37duZA/trIcZUjobZZ0TZhp2wa5T3ayDdHxrVMuFxkuQl9sWSwDZuOBd2P7FK/TEnpzGmSdOlV3q6izmno6ZmXjm 7ZxAyokp3TtF9EkSF5o Ut69YIhuht3s290M1cKyW3W73TQq9FVLoj G/etkTdd TthYb5Gnczk1eC67chEI7X2t5lpYEorUcxYUXRIjDpyNCD4slXdNl2rZB7pPtbUN2lpVYmlanV3aunYGZuG1TvE5M6C13QpSpunt nAuX N4Z0uK72Mf GCfxZ8Px40LfDJ7UFUH7FF4LoZ/0LpEG27WEQm FyUdP7opp2wa5T7a2DenqGnSnyfddEaURxoR8vkLfd5xhZzw5QOl5toNT9zYb8NyauQu9ReerBwq9FRT6 2TatkHuk21tQy5dHWwoa9HpyeTWYSTFK5oGutnfQkx1x1fNXhaDKVvliFhucOT0dkTUAN/2nhmm4OBdOyemNlHdx96kpP3BePVKI5nMxpYiQxJp 4PEaeM sPbRDz8b/Zk2gdNiVvboBaKftfTPF5dI6/1QVPdt82yfhufKKhjNHkyM5RfogUJvBYX Ppm2bZD7ZDvbkKPQfkFu4mq2EJ2xFK9Q/N3SbSc7E2pdRlK2NucYDiIs8w94X091y06IMt271YheEb5WlPwuQt9b493yLdQdMukKlcHLSvzFtsF4xriB6vet90dR46mKdSd q66X44hjfheJrZrfoHm2YgtiJe A2fUhMO1 aQGFnkwe2gbpYzvbkKPi/g577SeWjfYYlnvGy4Zd7Tx0RrEjKVttp23LPEXcCi502h0KS6Ev84/4IOMW6h08ZWDcfQt9T1Id6ZqRdbi10MvrtP3izW6S/zSsyNISWaE7OzJkD4OjdVOiIAso9ERjg/zyR9HYaIGA9wRtg/SxT6FvgsEsl91tkf3NOA3emob9PpqytTrHyKxivdumPi2uXHsnP7QUPCmasr77EPpdpu71fUwkWgfk1kIvr2Pah QIfvwPQzxHt259Qm/c74RCf1doG9N0EoNAecnVaZQN8uSl8MnMdZp/g/zDxyqz2XWME3domvNumJZtkCmxr6n7Q4o8YDOiN4iQlrLVSug7bZVhtHwroZejVMN5R4Lxhk8vp Ft9zboS5MrVzKJEfiBRvQNpsBNe6EfnOExwan7fWLagU5F/vja k59fe4s0RPq3H8E6rRsg0yJfQTjHWq6XqXjX6 X5Mk2ZDxlq5XQyxTHuj/ZIMjtNMiG21R8/d3cHthyed04reV1SkBdO ZA/cIBfPSmZ1P76JvlyGWe4u3bFHl5O6Hv uhHBlYMxtsnY0Ivflxt qT68e5/BHwbqoZQvKw3KcIjCj2ZLvtYXmfeGEbp5OqjqNEUr12MUfd6BsmRlK1WQq9nxHR9hK8DLQ2xKQ2y4UzSZ w0e3a017Pr2TeHNsyxpMyRvn2tnNNp bo77C3qXmJ Nt24BxlFf8sRvf8Sr3qi7k3T 1xet1cshV4zGLsXcdo0nZXfRPQxhZ5Ml 1twxCFTsgdY/TRj39LdCC4Yc4O6Ns4dnvSTa/wV3zpDczQixD8wTzwu Swl0ai1FOdAqrvS9 m02ZNKFqxB67/Ai 8o3vfI59CT/rYyTbkVOy2a7YJ2RO7Cb1t7pQuFPrazyTXQCpBdr3BeLYj rE88DvksMeAv692JYjrqlNBItf98JrQaaa8odCTPnazDTmq39ce6oRsx05Cv04Q7Bgc/cCFvicKV4t23VnoR/PA75DD/sYUsaktdZEBJZ0Ry9ia0Gm6HCj0pA/aBiHjPHChlwKpr/scW15nKfSjeeB3y2Hf7Q221wd31s02NRxZEzrN/Z3ZmJM aBuEjPPAhV4K3x2O6FvslsN TOi3HdFPHTbmpA/aBiHjPHChl5vCKClbD Kj78sDv0sOewuhN/noi6zKcT 4JvSAD/oWsDEnfdA2CBnnwQu9Oer b4iCH5pR9c5Cj5E88LvksLcRetN1m5mF/jWhh3vKt4GNOemDtkHIOBR6MnloG6QP2gYh41DoyeShbZA aBuEjEOhJ5OHtkH6oG0QMg6Fnkwe2gbpg7ZByDgUejJ5aBukD9oGIeNQ6MnkoW2QPmgbhIxDoSeTh7ZB qBtEDLOpISehYWFhYWF5XCFQs/CwsLCwrLgQqFnYWFhYWFZcLkXoSeEEELIdKHQE0IIIQuGQk8IIYQsGAo9IYQQsmAo9IQQQsiCodATQgghC4ZCTwghhCwYCj0hhBC yYCj0hBBCyIKZgdDfII fwXE8hGlxwOsUSEMPzlGI9AZAHsM/ DUfIPf5XG9ShEcOjsIUNwc5fYgj5xni/Ebc5xH8 MsBrmRVGYRHd3X9u3pHb0f1 yrjl8Q 0dw/Bj5Hs7W4cC2unzE7yPb83u 3n5tb3umIfR5DL93y7//jf/4j/99940Ihf4wbPVcSxTZfyEryoNXax 0hH4vrJGln7CTBd5K6C2ee/EJabaWF6PQ70LrGY4xr3fh7tGfz22Ffuzd2/f1Dss0hF6h zLeUyNCoT8MWzzX/QvnYdlvfcUM065CcguhH72P/9ve9bu4kWzr/jc6nnQyZxspUnKTm2zioBcm2cCZg4YJHhieYcCCgYULDwYEgyNzTYPhJsvwxPJg4TEgzIJZBoHZNWboy7LsGiGWQQzNd4Ou6q4fp 6qrpJZG0pwvsqVRd1WdU erPlV9PuvaTPQrNCbKPvs2F7YNe3zWId7uudfv/TYPJnoXmOg3Ayb6QDDR9w0m sMFE70fPRL9HLPiFAORck zf C6XEZfxU30x3ia/R1pkiBJhsiLG5FWqbCYfY9RdixS/SkGeeFIcZl/e4xs9L34W3Gfzj162Z4h8tFz0d9jZOc/oqyA2uDHGDx/jixNkCTfoij/wOzqXPxfb39VXuF0kIrPxf2qW0xOh832xdFointXcD0aYXov/j14hjw7RiL3hhczXI0yMWYJksEpCjJVGNdmYIny h/iuxSD/CXyQSr2E4lJoo6lNq4VFrMCuex/muH8ukQlJ426hZMVKEPsZ46B1c jup3UGFMOubhBkQ/b zV2NtqSZjg7y5DKya/ay2s7wgeKsbGVFWBP7btjZGcvkKUuIokdd9P31bZ9i6K862eOLq4xGqRI8wnqXv2OSf4ESfI3jKZf6r ZT5CnxzgpPqEyxiPNznHV Lft02 Kl01sqcofcZ4dN78h56EXYqwGzzGS/tGMo5sIjkb/j8/kGJreJ// Dd54bdL bZqd4ULz1X9h8lbE5PQE4xs5Ng77W NfYT45RZo Q3FLxHLv C9RTl 392hiW4npZd7wRHI0wvRuhdhm2sEaH/F5 ndkT4 J OfgK2sbuaf7KXEv3tfWR79EL/c05hPkaYrh AaxO0puok8xOL1Cef8JxckxkvQUk3klgsMTZOMP9b0XHzDOnpD3rm4LnKQJ0uwSN4t7LG4ukaUJ0pMCt1Uo0cs2yuvc4bZ4hjQRw adxhCFOJ7eoUGExPcegmWiVuO/XGM9 r0lxcI7pogIWnzArl L6MrjN8XH2G6oQopdjVAHAF0xHfxNtrADMcTM QTocY2YZJabNd8K Zv TFYle7nOJoK60zwyWQfbTxoDu59FoijtqjKmfNPuoIuglYgxkUBTjK4kjiSb6BekD9lOFz571d00wr0pcn2dInYcB48bdgvOJft0 5eofZ Ov2d/MJ8vQJBoMjQT6SeE4x fMXcQ/R58UHjLNjJA0pmT4t /UV8otzZKm62HDZwAd5fTHvK73PbqIXC8rOJ3r97/02adtSj/GymZNpdomb c8YD1PFl1z2N8ZffNcSv4Kmv/T4V7MxhurCePEJs3Iuri8XRBUWHz iXMbGNhvOJ2xh/3sZO5q PhqjSd61/2auPfvFXxtffRH9ObThu8pyYPu1L38fz3IknStQ3yWkaj0ojCo lQSTPRPkE9 lx9gdKSv7FqHkvcw23iErPhVkNUxslGBqTS4mDRpNkIxrZ8Q/GQh/t1MUKVN1n3dTw9hbf7s7H880c NrEGipb70yRRoP3UMLCjBkxrEl0ohAAATsElEQVRjC aTaLsCrwOZMgbNQiCW6CvaB8xx9Nnz9gPGw1QPyPMJcucTfcy4E hM3a86R6GM62/1eA4vcH0lyH3 W0s84slLjTH1fWS7TJ G1o56cajYmbSBD2aqVtq/9okHIXo1bVwWyBJJXub3HvurGROx0Gp9XIF3/GfGgkEO843tp RYdMQ2At2pdGOrxctXfaTujfs1cW gq tj56IXqwE5epZGHQbRG8HXOeVCaKQ7e6H6GsHNia0 ZRCYTHDZJxjoDx9AHPMJmPkg6N6JbucYnSkrjrFddXJoE5016QiEdfmIKJXnhBrG9lEX38uV pqf9T7 IjeY7 gfhpjbKWA6jFMBi8wKZdaP2w/7SJ6l 3Ezy0fMIKNz57Uq1geoo8bdwKRRB8 R9V vsbb/Kt6zCThvH3dEg9BNPV9dKK3iegr5KNTY665bOCDi hV/xDZH6VfGyV6a3Gtj0WzVeS1v3zC/w7FhSduecd/FaKPiG0E4oi3i682SfQiXkT52vromei/xnj2V5323dITfeM8zZmAJcrp95gQe9FW6lfsU20idW9PACWNVZWYvvsBs8UdyvcfRGqr3R/7s/yA9 USMl1bT5hfxT6cTBWLfR7nZLgz0mRAVU7xbjIjXhmJaXPVpu5PCtxWS5STF4q95QpcppHlXrib6Ifjm2Z/0Cacdn82yn4k2n4uyTE2ppskejU9LvsRk7pv9lAp2y1JH5ib6WSvPeNS97HjTkwAjI5SDEbXwpf6m6NtLElEPLlDu1eftHayUsfi LIWRureJfoDR9A/hszLIumzgg7E1YKTuaz9vU n6HKHGkL6 TvQum6xG9LT95YJFZD5c49Ax/nbq/iOms9/s1P3sJ8wWsbHNhj0 IUTv4itz7q17Pyhx748VfG199Ja6bwNdgjR7jucDuScUdyI3mugBVOU1LvP2YJX70Fkfh/FkG4 R5c8ch/GOjEWOeTBF7g 2 9vqgRBJaPoBH/sAzdlZJlKaS3oymAdftANSKmLaXEE/jNfau/m9eYDt7AUy7UmsPZhTE1KCJH2K/PlQ31qQ 35NajHCfiQUoifH2ITaT2lvGTxte4wucgwkOWlE77Md7QNtOllJK/rsaY756DvkgyP6nEz0uJsXEOcDmq2MLz3OUTQLyTYr1JKPFhQ7D O5iH6h9GGI/PL/cP1PYh4KsqoX8LQvtYfETD8yD3u9wFl2rO0R62Nozkqj/V6bxBF9t/0F asZCQpRh/HE/Dd9OD3FZH4fH9ustpjj4ydeN18B5Nxb834q0dPzfbPYudfr9gEPXeVo58BVvGxstTIdo3 E7Q0fJuztN8Z g4l BTDRq6lXmZYM3IM9eFRYzH5AMc55TPYanhPnB446df7Ekclg7COY6FcAE72adjS3Lh472nfN21fhGIx9gHyLxf8qG2P/wETPYDAYDMYBg4mewWAwGIwDxoETvSE9u1Fsst53x4ly38Gvh5ZL3VnE1ZJfr9b4Nv2wr5rbEW3uOowZfFiTevtjD7HqQcxe9TVs 7WlVwPvQbwrvz2EvVbHCMN Ez0l8xgl/dgnmOi3jzVkXLdK9JvELsplriqpykS/OSGtkJP0xnx6lEQvX4v02M8lq76OZPGGsb9ET02mB32liYl u1hT3e1AiH4XVbRWHysm s0RfdfYukpXHzjRVyWmlyOMzboeMTFzcY2Rq2bFjoCJvr8GMdFvFUz0ABP9TmIXib5z SREX1TglYpWrO4QXH6Xxh/uIqwnyF2taPYGaKnpftM8YUh8uIDZpbM4zd49eobW xDq3/eyss z5 2cp5SUQt6taRGfpJ0tLakZVsZqUtOF95KUn4RDMPpYyRJhbiFlJK1qjEFS9na1c3qtsVKx/5CfParV8bUum W4WvN1rLvlL/I8de/k5XKaKL3S9AG2Yrqc69 uIY8p3OMVFAKYq42d0mqmlXeXNK/HqIvC2Tq/bMCn0Ps4Bln2 aUdC/aOdRI3hqvTvYiEQy9PLRLytRbjY6y30sUb8x4aSwmXNKs4vP0aYanjSS1Ii8cFDuIEtOqcI5T3pxQeHQJZcVIlTcEn2KQX AdJWgVs1AL0RTx2Yzw602k/3eE6CmZyDu/VGrQE72uEtaU0TwpcFuZDijqaYv7NWVoKaLX6lQLqUVTJtWU6uyQdQwn khJUjmJZQ1qTT4xQsrWqldeS7veR0vHEp/5ZEwd97VEX7zSurKetVJ7XJa2pSZWRx37IFtRfe7bD F5oiflMjvkh/UrR7S5S4DFJHqH9G8n0SeNwJCv73IB6m zCY90ryzJmz5DcSviUlMMqUeJ4C4p044Y4rYf1nqir8d8IUq36v0OiR21D8vfKVLD8/p3tFxsBNEHyyDLOgEdhayCib4yfIH6kw6bEX69CewI0VMykX6p1HiiNwvdGEFGU6BDe39fre80w6iYGgTmqPfdIasZTPRLYgXpky S17iuJ5BSTP66DpWxpBbJVpGPt0qI GdNbp/KZOfl9/kKpaYlx8Eql0hK0Qbai ty7H8aqaHXMKf3K4W2OInq39G830et 0LWg8LfZhEe61SRJlZCoJ7pVJYK7pEw7pXnd9uslda9uA0bJYKsLGqPioFMuNpzoo2SQyyneNU/0Y1pYKZjojYUahS6bEX69CewI0Qto0n0fceOTd12b6I3/RwbYemU wTgfitXYX9FEr8pq mUtlX7cxUmSOonetWhwIJzou6Rj7b03n4yp ztz8vukdSlbuom S4I22FaOPvfphyvJcwbVb49ocwzRe6R/u4leTzl3ScH626zDK91qkqT6/z4lgrukTDuled32653oo2Sw20XWRfEdho3qm08uliB6h/R1lAxy011ij74ZujCirzMVqf8QXpfNNnoAs8WOED0tE/mnTyqVknl0yWcGBSv5pCtS3JpUotHcqsT790JRrknd/LtDqrNDVtMra9lD6l4GVi2VGyFlS6TQZ9OPmEdLxxKf WRMHfddEFKSbmnd 15T9 G2ovvcmx82vw2Xy/TKD tXXpPo7TZpRE9J/0YSvd8OqxE9Kd3qI/o JYK7pEw7pXnd9gsmelWa1Uf0UTLYaCWfk0QhbJ9cLHFGxCV9HSWDbHZ7hslYnLpvhi6E6AMXzUFx/xERPS3d55NKpWQeHfKZQcHKOAQl5RtJohfG0w4Tdcvp g/S GQtzcN4EZKk5EEiZQUbLGVrH4pr9n2jpGPp07Q GVPnfS0pSb /6ON7hot86Ei7dUjQxtiK6HNvfgjEy2V6x0jF6kTvalNjI6f0byTRd0jBxhC9V7rVS/ToTyI4RMo0 jBeKNET88lL9IiKHS2p60/AnfLmrpinSl8jUga5C67MsJZtidCS7zyM92iIfhexzWpmDIYL7IcMBmM9MNErUFNPMmX6GGUqGQ8L9kMGg9EnmOgb6KkrK2XGYGw F7IcMBqNfMNEzGAwGg3HAYKJnMBgMBuOAwUTPYDAYDMYB45ESvfnK0QPhQUUjVoD22gnx iBjo9iOsE6Pp/yDdej7wO69neB9nW8tyOpyV/g8OUVKvke/LaiFdh57TFA0UCL9UPOVDbxyt/tET72reXktys6aIEp8kgO DaKXTk ViRSFWvaa6PvAqrrl 37v1bCrCnoMiS351HyCPH2CfPKzVoLVLgXri5V9YV0VSeqSUgth21jTfqJg29pytYdL9AtMxyNcUkpCmGM2 V7Ue5YFMlzlDkNX9dt one065ET/UMS1z6S5j62 TFhO/ZpS0y/vX6jlWDV7y fLjddR71non9AqfG17dcXQR8u0bfVstJshLeuMopARzrQXb9cBxP9SmCif1DsY5sfEx7aPtb9t0KaTPT675nou1GVmL67qMtzDnK MLcLvkgU0NLqdZRDF30mtb1HmtNGF9mlG4zOK7FgpKRviGH6ip/WeQzWWKf1zv767DpceNDp1ttWJ4RcykbWpZXlNh265rF0 k4f 6srvBV2cuuAq/b2aZG7dNwj/IPUkPaVAoa9BSXkX912Mr5LM5ydZXEKeiv5hFp6VNlzdG6DqSVtUwzyl8gHUphEtukaX6x5K/aZTwrcVqaim1JKtUsLnmx3hBa95ZuyrK1ba90st r3Z5dmuuEfwf10Q/cJOa8V0Z8g/XjAH/90W8myw3IOBccEmL71EsUbc6vzWxTlLyiyo7ZkdVN2/F YvBVxq5Fd9vVx3Zhg9z1JM4yuZvTvrbkSYv9Ht0cvB87orBSBUIUXNEit8raiGC06IK9/jJPiE6rK0I73aUYbet9h09BP9KTec7DGcqS OzFmtB50t1hH6KS 00ROWhtZv5Hj0dxTagrUE3KuKXX59LC7tcj9q3d51kMEgsY/3BrSlSnuI4re1Pc3BUAqLD5 RDn32KlDWCeI6FfyCVMpUYpEiTabDiS02ut23jU12nWin JejGFT4a/ZZ/6tXrw3wVoWDBIE5dWCd7T7PlyL/p70TY9v3dsiS35/FgprXv9ARD/dsPboVQKM0I93x7 qUxwqmOjvHb5lPdG3sVreU/pYml3iZv5zLZaTFSg3GhPkfWU7pK6K4BD4n g77f oiN73RC9X3sEnTOVeFjVgpvCHdAI5sTya0eK3cSVJA1P3imhEuMZyjL77f OVuvLMCpQuPegAne3gSS1ETtJshEI5h Ei nYrQxKWCPrq9x162F1a5EFEb42pS0OakuuVi4VvUdx ICU9fTa taQ3KancDqIP8gmHPx2NML0XwSzNMCqm5KGu rpKO7WtNV2HvrXBX/W/01NM5nP7AG2SiCzEZ N6MBajrnabQdejRU/5pse3/vm// OURHUT/Re/f1DCOc5 uqHev37QOWqVPJ19 gavXn1jzJ8/HPGPUmzTt0vDn gdvuUiejV2iuxHPTbK93ebjAlEO SYan2n KYjPmiCRgdN9MrKkErZNySvrlC7sArRq/rGDs1on8KWE/FEH66xHKfvrsOjBx2gs21Parc2eH2ocox8cNQ8ZdKBkVKNUieDZyGijkqHctlqRC/G1JqI1ERuD025iN5nJztoUETvGu91fML8bYXFbIJxPtQyGHo7Q4geLXldvMHFUJJQh9xnl3Kco91RynWmb967favbZqFEr/hHiEJeAPT7G MaoR/vjn9UHOsiel9MIHzLRfTqglSLE0osX24yJhBEL6V3VyJ6w/6Pg g9p 6l5CURZGzMMfvhPcpKSd2TaX4j/W6k7r2a0Vsi nCN5Uh9dw0 Pei41L1PG3xZfsD7cglAT5dZuuUxRN hhx02qVXNdMJe3tS9PhGt1JzY43Sm7mc/YSbSjqSdOlL3fi32dXxC e2yxPv3or2uVLJM3Z8UuK3MdphzRfpb0mZpIIlFyj1DZPZ qFPHGyb6ivTNv9y ZY1ju/VF 7Mjda/5B9GvtYkeRlYgXD/eHf/iUvdeH60cvqWl9IEoor/fZEywU/f1GYgVU/em/R8H0Xsg90PJlKO5UhKry aw0WvxWp4JedhKHlYyDpz4NKMpou88Pb8C0SNUYzle312FWw8anTrb9OEf/ZBOmk/wp3Bya5xN3fLPMUQPrx52Z6C3NNMJezW2N9pNTsTIw3hyUem0k30ganSRK4erfFrs6/iESvTyjIQ8APUjkb5XD O1PkQTvSSRRDnzIq4xfd32VT0ouGmid/mmx7fMcWyeIEl/DjyMtwmil/FQLlBD9eO98c/0O3FITnuXvzsmzCuXb8m970TE9Z8jiN5vt/ViQt02 jAe6Ovpg8qH8Rj7iYd nWhz2L0qa3uDrVbDY waDjcm7DeY6BkrYI7ZpKj31lx7q3sNJvpwqFsA2yrSwtg9HHpM2G8w0TNWgPnKy6GBiT4caqrVl JnHDYOPSbsN5joGQwGg8E4YDDRMxgMBoNxwGCiPwis8sofg8FgMB4DmOgPAjFEv3/yrAwGg8FYHUz0B4FwoufXXxgMBuNxgYn IMBEz2AwGAwau0P0UqZRyFzWlZRkmclI2U1KepL6zKqrbFQUo RIg6UeKTnbpVcqVK1S10ikqjWmrepQsnqSQfRmRbvzH1FWHilGo09pdo4r2SdSkpXBYDAY 4LdIXqpBCRqqze1gU8K3FZxsptLQnqS qwKIvpEqbMfI/VIyNl6pUJluUq9/6sR/UdMRRnVToWmpo67qGkvy0B6JFkZDAaDsT/YOaJvlYdUGb 7ONlNSnrSKUfZRfS2MpdLBlGHLWfrbbOr/9FEb9ZUljWjHQpNRJ1 vyQrg8FgMPYJu0/06Skm8 UKspu2LKr12bJWSmo1nw1JWlNcIELqkdo397Y5hOiVzEF9LYLopXSieALX/y6M6OvfqETfr8ACg8FgMLaHnSN6b o UHaTkp68uvmJkKP8tX7qbqRAhbSti gjpB7JA3JeqVBdaUpvi h/Ixkrzxt4iH44xqwSffVJMVqpe7G/75FkZTAYDMb YOeIvpFKpQ7jBcpuUtKT96QcpS0FenaWIZVbBBTJhUo9Ok7C 6RCtcN4Uh5S9tk8YHf2AlkqswPqvVTZ0GNk TMMVOlXSoqx8zCeOgamNDCDwWAwdhk7R/Rc3U2ChVUYDAaDsT6Y6HcI6jaATN2HnQdgMBgMBoMGE/3OoMLi5lKk3BNj64LBYDAYjNWwO0TPYDAYDAajdzDRMxgMBoNxwGCiZzAYDAbjgMFEz2AwGAzGAYOJnsFgMBiMAwYTPYPBYDAYBw wmegaDwWAwDhj/ARJ6YT9sy3kYAAAAAElFTkSuQmCC

miz
27-04-2019, 06:18 PM
what should the setting be on the low oil pressure trip.

and yes there is discharge sensor mounted

the oilfilter in the oil sump is brand new and the other one is altso brand new and the same goes for the oil reflo 68a.

you could be right in this assumption with the screw and piston rings . one thing that i have noticed is that my discharge temp is not rising so fast as i want it to.

could this be a indication on that the rings are gone on the capacity control.

RANGER1
27-04-2019, 10:54 PM
Miz,
If a Grasso RC46 is the same as this in link on page 16 then 1.5 bar minimum oil differential.

https://www.gea.com/docnav/Product%20Documents/Grasso%20Piston%20Compressor%206/0089238.pdf

Has machine been overhauled, or valves checked since installed on 2003?

I thought on start up machine would be at minimum speed, load compressor, then ramp up speed!

Can you prove unloaded function correctly, sump heater & oil return not returning liquid refrigerant after off cycle.
Maldonado if machine shut down, does discharge pressure drop quickly, as could be valves or unloaded


https://www.gea.com/docnav/Product%20Documents/Grasso%20Piston%20Compressor%206/PADOR9050.pdf

miz
28-04-2019, 09:42 AM
i will correct the min oil diff setting to 1.5 bar

mashine has been overhauled in 2018 november and new valves mounted at same time.before overhauling oilpressure was fine and no oil diff problems but we overhauled these loading mechanism and that is maybe giving us these problems today.

mashine is running up too max speed with no load and then down to min speed after 10 sec to min speed and when reaching min speed 50 % load is put in and first after it put 100 % load on it will ramp up in speed

sump and oil return heater is measured and they are function as they should and one way valve from oil return line is brand new and controlled and is working as it should so liquid ammonia going back to oil sump in compressor.

mashine is loading an unloading as i shuld on both 50 % and 100 %.

cricri
28-04-2019, 03:20 PM
If there is no high discharge and oil temperature there is no problem whith the capacity control, it's a gas operated mechanism so no relation with oil pressure.
are you sure that there is sufficient oil for operation at low capacity, poor oil return from evaporator and low level in oil sump.

If this is OK, you should investigate arround your chiller for liquid suct by compressor.

miz
28-04-2019, 04:57 PM
what is the max oil temp on these i think that my oil temp is 60 degres under load and that is with brand new valves and no broken rings.

maybe there is a slight mailfunction in my oilpump it is only coming periodic the oil diff alarm

i have no liquid back to compressor for sure that is measured lots of time no cold suction line.

for not so long a go we had the evaporator fixed with new plates and gaskets and we drained all oil from evaporator and we practicaly had the problem since then. could it be incuficient oil in evaporatator and oil return pot .

RANGER1
28-04-2019, 09:24 PM
what is the max oil temp on these i think that my oil temp is 60 degres under load and that is with brand new valves and no broken rings.

maybe there is a slight mailfunction in my oilpump it is only coming periodic the oil diff alarm

i have no liquid back to compressor for sure that is measured lots of time no cold suction line.

for not so long a go we had the evaporator fixed with new plates and gaskets and we drained all oil from evaporator and we practicaly had the problem since then. could it be incuficient oil in evaporatator and oil return pot .

Miz,
Grasso information indicates oil at bearings 10cst & above, depending on oil type.
If you set to 70 deg C, I think safe, as Sabroe & other brands are 70 deg C.
See page 23 of my second link.
Maximum discharge temperature 155 deg C see page 5 first link as well as other important set points with loading etc.

Maybe check pressure transducers for zero at atmospheric pressure & if they look like working properly, stable etc.

Doubt oil pump problem if you can set to 3-4 bar when at operating temperature, but anything possible.

Any high oil consumption issues?