deyna
12-06-2006, 08:55 AM
Having problems with two Profroid WPL 2 fan condensing units. We've had the discharge line from the compressor into the condenser fracture on two units, has anyone else experienced this problem as we are hitting a brick wall aith our suppliers who 'suorisingly' have not had this problem. I'd be grateful if anyone would let me know.

Thanks.

andy bailess
12-06-2006, 11:30 AM
Only ever had this on the WPL 22, we had to fit vibration eliminators to take out the twist on the compressor during the stop and starting cycle.

Peter_1
12-06-2006, 07:09 PM
In previous posts, you can see a lot of posts of me regarding Profroid.
I visited once for 2 days the factory.

All what has a coil inside is not their best side.
BESC5240 and I had often problems with a lack of capacity. Capacity given in the catalogues is 20 to 25% oversized.

Icefrog
14-02-2008, 11:03 AM
In previous posts, you can see a lot of posts of me regarding Profroid.
I visited once for 2 days the factory.

All what has a coil inside is not their best side.
BESC5240 and I had often problems with a lack of capacity. Capacity given in the catalogues is 20 to 25% oversized.
In fact Profroid data's can be boosted on their literature up to 40% and this is confirmed by a test performed by the TUV laboratory in Germany. If you need a copy of this test I will send it to your private email. Since in many case the impact on TD or operating time is not measured, they get through this. Go for Eurovent suppliers.....