View Full Version : Charging system using recovery machine
Contactor
01-11-2018, 03:02 PM
Hi There
Can anyone give me a good reason why it would be a bad idea to use a recovery machine to charge a system with refrigerant, apart from the possibility of oil contamination?
Thanks
Contactor
Tayters
01-11-2018, 03:20 PM
I can't. Since the price of refrigerant has gone through the roof that's the way I do it now to get the dregs in.
cadwaladr
01-11-2018, 06:56 PM
I have done it on some car aircon when I could not locate the suction port only a delivery port
Rob White
01-11-2018, 07:56 PM
.
The machine does not know which way it is pushing so if the
machine can do either direction I see no reason why not.
I always advise people to push it in with a recovery machine
especially if you have a lot to do and it is cold, the days of
trying to warm a cylinder to get enough pressure to charge the system are long gone.
Rob
.
hyperion
02-11-2018, 01:55 PM
Suggest that you use a liquid line filter to make sure no impurities get into the system. Otherwise as has been mentioned, it is the best way to recharge a system, especially if you have a lot of gas to put back in.
Rob White
02-11-2018, 04:52 PM
Suggest that you use a liquid line filter to make sure no impurities get into the system. Otherwise as has been mentioned, it is the best way to recharge a system, especially if you have a lot of gas to put back in.
Good point and I'd offer you some Luuuuvvve if I didn't have to spread it around :D
Rob
.