PDA

View Full Version : Daikin vrv REYQ8P-48P



eurocooling
25-02-2018, 01:05 PM
I have a fault code come up on a display of E3 which says it could be

High Pressure
Defect of high pressure switch
Defect of outdoor unit main Pc board A1P
Instantaneous power failure
Faulty high pressure sensor

Where the best place to check first as all the zone areas are coming up faults also where I live the Daikin back up is terrible
Or does any one have info on these units this is 10 years old

frank
25-02-2018, 03:06 PM
All of the indoor unit controllers are reporting the fault - E3 High pressure. As reported somewhere on the system.

First of all, check that the outdoor fans operate and that the coil is clean.

Download the Daikin App for your phone from the Google or Apple store (free) and follow the remedy for the E3 error

eurocooling
25-02-2018, 04:43 PM
Hi this is of one controller and you can control the system through a lap top

r.bartlett
25-02-2018, 05:05 PM
I have a daikin service checker here in Tenerife if it gets that bad

http://www.daikintech.co.uk/Data/VRV-Outdoor/REYQ/2007/REYQ-P(7)Y1B/REYQ-P(7)Y1B_SM.pdf

frank
26-02-2018, 03:14 PM
This is the App https://play.google.com/store/apps/details?id=com.daikin.aircon&hl=en

You can download for phone, tablet or PC