View Full Version : F Gas certificate for water chiller



bobjob
31-01-2018, 07:52 PM
Hi All
Can someone advise me regarding the paperwork for the chiller below:

I have a water chiller with 2 refrigerant circuits - each circuit contains 16kg of refrigerant running on R 407c .
After leak checking the equipment I provide the client with a separate certificate for each circuit, therefore 2 log sheets,- this is done every 12months

The client has informed me that I should be doing a single log sheet every 6 months because the charge is 32kg which would be 56.77 tonne EQ CO2.

Have I been doing the log sheets incorrectly?

Thanks Bob

Rob White
01-02-2018, 09:58 AM
.

Hi Bob

You are correct, it is per circuit as long as they are completely separate,
they can share the same chassis but the circuits must be separated.

When it was the older 3 Kg weight limit, multi deck manufacturers got
under the weight limit by putting two smaller systems in, both under
the 3 Kg.

Each circuit as you say is 16 Kg so the individual C02 equivalent is
28 and a bit tonnes so you are correct in your two systems once a year.

Regards
Rob

.

bobjob
01-02-2018, 08:22 PM
Thanks Rob for for the answer

Rob White
01-02-2018, 08:51 PM
.

Unless they insist on paying you lots of money to do the second visit

:D

Rob

.