View Full Version : Mycom squealing shaft seal



RANGER1
11-01-2018, 08:07 PM
Anyone else experienced new shaft seal squealing in compressor after overhaul or seal replacement?
Have had on a number of jobs, are we the only ones?

NH3LVR
11-01-2018, 08:55 PM
Which Mycom compressor? Did it go away on it's own, or did you have to replace it?

RANGER1
12-01-2018, 03:03 AM
Which Mycom compressor? Did it go away on it's own, or did you have to replace it?

Sorry, forgot to mention screw compressor 200 & 250 on various occasions.
Replace seal with another brand, problem goes away.
When remove seal, do not find anything obviously wrong.
Only happens occasionally with Mycom seal & another after market seal.
Had a Mycom oil pump M50P squealing, sounded like a tweety bird whistle.

cadwaladr
12-01-2018, 03:52 AM
Always best to replace with oem,slightly more expensive but you do have a come back who cares because the client pays at the end of the day cuthing corners bites you in where you don't want to be bitten?

HVACRsaurus
12-01-2018, 06:10 AM
News to me

RANGER1
12-01-2018, 07:46 AM
Mycom even mention it in manual
See chapter 6 go to 08 in troubleshooting guide.

http://www.mayekawausa.com/pdf/tech_data/160-320SCV.pdf

HVACRsaurus
12-01-2018, 09:36 AM
"Squeaking"

Rofl

derfriguy
28-04-2018, 12:44 AM
hi, yes had this problem recently with the bellows type seal. Seal was replaced with the boss type and the noise went away.

RANGER1
28-04-2018, 06:14 AM
hi, yes had this problem recently with the bellows type seal. Seal was replaced with the boss type and the noise went away.

Was that a Mycom recommendation, or your own, who pays ?