PDA

View Full Version : Panasonic 3ton ac



OkonedoCharles
30-12-2017, 07:47 PM
Good day everybody!
Panasonic outdoor keeps running and does not stop even while the indoor unit is turned off.

The outdoor only stop when the main power source breaker is switch off.

I'm suspecting the indoor board/ panel.
What could be the problem? Thanks

frank
30-12-2017, 08:07 PM
Model numbers might help us to see what system you are talking about

OkonedoCharles
30-12-2017, 09:50 PM
The model number...CS-C28FF
thanks!

Brian_UK
30-12-2017, 10:19 PM
Probably a power contactor stuck.

OkonedoCharles
31-12-2017, 10:23 AM
Thanks!
But the indoor takes the power from the power source,
While the outdoor takes power from the indoor.

frank
31-12-2017, 01:17 PM
As Brian says, it is probably a stuck/welded relay. You will need to trace the power from the indoor pcb with a multimeter.

OkonedoCharles
31-12-2017, 02:57 PM
Thanks!
I will do just that

vikky1971
02-01-2018, 06:23 PM
15077Brian is right. The mag. relay must have stuck in make position, once you tap it, it may start working but later it would again start giving you the problem. Find the picture of the power card, I hope it helps.

OkonedoCharles
20-01-2018, 08:04 AM
Thanks a lot Vikky