PDA

View Full Version : Daikin Vrv IV



ronaldo9
13-12-2017, 04:07 PM
Hi guys,

First commission of a Daikin VRV ,
I have 3 systems , 2 are working fine (3 pipe ) but one is giving me trouble ,

2 x FXSQ 125a ducted units
1 x RXYQ10T7Y1B

The system will run but won’t clear U3-02 fault from test run , I have ran through the auto charge procedure but it still comes up any ideas ?

Only thing to mention is two remote stats have been fitted , system runs fine but fault coming up on controller . I need to be able to hand it over without faults

frank
13-12-2017, 04:46 PM
Are the only faults the U3 -02?

The error is with fan coil 02. It will not pass the initial TEST run if you have faults, which is what you are seeing.
What do you mean by '2 remote stats'?
Double check your wiring

Brian_UK
13-12-2017, 05:50 PM
So the test run has not been completed on the error unit.

Did you restart a test run after fitting the remote sensors?