PDA

View Full Version : Daikin super inverter



Craig Johnston
29-11-2017, 07:46 PM
Hi guys, I'm having a issue with a daikin super inverter. It keeps showing a e4 fault. I have decanted the unit and charged by weight. It was all ok. I have checked my pressure transducers and they are fine. I have also changed the board ( swapped from a redundant unit)
Whenever I arrive it is in a e4 fault (low pressure) when I reset the unit it works fine but the condenser freezes up very quickly.

I'm guessing I have a restriction or a faulty eev.

Just like to know your thoughts.

Thanks

Brian_UK
29-11-2017, 11:44 PM
Have you checked the temperature sensors?

Craig Johnston
30-11-2017, 07:14 AM
Yeah I've changed the thermistors but again from the redundant unit.

frank
30-11-2017, 10:38 AM
Whenever I arrive it is in a e4 fault (low pressure) when I reset the unit it works fine but the condenser freezes up very quickly.

I assume that you are in 'Heating' mode?

Craig Johnston
30-11-2017, 10:59 AM
Yeah. It's on a biddle door curtain so the shop would kill me if I put it in cooling.

frank
30-11-2017, 11:02 AM
Do you have a full model number?

Slim R410a
30-11-2017, 03:07 PM
Low pressure sensor?
http://www.refrigeration-engineer.com/forums/showthread.php?16624-Daikin-E4&highlight=

Craig Johnston
30-11-2017, 07:08 PM
Tested the low pressure sensor already. Mod rzq250c7y1b biddle is UK.city m-200-dk-f

Brian_UK
30-11-2017, 11:26 PM
Have you checked that the Biddle unit is clean and with the correct airflow.

Craig Johnston
01-12-2017, 07:18 AM
Yeah filters and coil clear with great airflow

narkom
01-12-2017, 08:37 AM
What is the outdoor temperature?

frank
01-12-2017, 08:51 AM
On page 24 the piping diagram shows an expansion valve feeding the outdoor coil in heating mode. This may be starving your coil and causing the low pressure fault http://www.daikintech.co.uk/Data/Split-Sky-Air-Outdoor/RZQ-CY/2015/RZQ-C7Y1B/RZQ-C7Y1B_Databook.pdf

Craig Johnston
01-12-2017, 12:14 PM
Cheers Frank, thought it was the expansion valve. I'll replace it and keep you updated.