View Full Version : Sanyo H04 Fault Code



skilts
03-11-2017, 07:35 PM
Hi Everyone, does anyone know what the fault code H04 on a a Sanyo vrf is, l contacted Panasonic and they didn't know :confused:,

Many Thanks,

Skilts

Tayters
03-11-2017, 08:18 PM
I looked on the google and got protective thermostat for scroll compressor 1.

Cheers,
Andy.

skilts
05-11-2017, 01:20 PM
Thanks Andy,
I think its crazy that Panasonic don't know,

Skilts

Tayters
05-11-2017, 10:29 PM
Yes, you would have thought if anyone knew it would be the manufacturer, think it depends on who you speak to when you get through really.
If you manage it, Tony Duffy is the man if he's still there. But tricky to get hold of, probably made a rod for his own back knowing too much!

Cheers,
Andy.

Loops
15-11-2017, 09:45 AM
Hi Sklitz.
Sanyo H04 =
Compressor 1 has a discharge temperature in excess of 115°C
Most common reason is low gas charge, or high diversity or maybe faulty discharge sensor.
I was the last Tech Manager at Sanyo AC, and now work for an ex-Sanyo (now Panasonic) distributor ESS Aircon in Sutton Surrey so if you need help look us up and give me a buzz. We can supply Sanyo parts too.

Cheers

Loops (aka Lewis)