PDA

View Full Version : high superheat forsab 28 cmo







dolce
31-07-2017, 06:55 PM
Hello Friends
i have sab comp. type cmo28 work with R22 when it run full gives high super heat 135C
it has not oil cooler or TEX for injection liquid . is that normal ?

FaultCode
31-07-2017, 08:34 PM
Possibly not, read the expected temperatures here...
Page 57, 58
http://bit.ly/2uOtFTF

dolce
31-07-2017, 09:29 PM
Possibly not, read the expected temperatures here...
Page 57, 58
http://bit.ly/2uOtFTF

Thank you for your advice

RANGER1
01-08-2017, 12:43 AM
It's (almost) impossible to get 135 C superheat under normal circumstances.
Check suction temperature sensor & its connections.