27-06-2017, 12:24 PM
Hey fellows,
I've got a Mitsubishi heavy that's gone out with a fault code E42.
It's pretty vague what it could be.
It's basically over current on the compressor.

I checked it out earlier, windings on the donk seem ok, it brings on the compressor for maybe 20 seconds then shuts down on fault.

The compressor sounds a little rough.

Has anyone seen this before?


The mhi tech docos are very vague, could be stuffed compressor, power transistor, eev,
Closed service valve, etc...

Cheers

frank
27-06-2017, 08:01 PM
I checked it out earlier, windings on the donk seem ok,

What do you mean by OK?

Sparkletron
27-06-2017, 09:51 PM
They aren't shorted to earth, have the same resistance leg to leg. About 1.2 ohms stone cold.

install monkey
27-06-2017, 10:34 PM
het an inverter checker to test inverter circuit- if you say comp sounds rough its prob pot siezing up causing excessive operating current thus the e42 fault- how long does the comp run for before it stops?- maybe clip the incoming phases to see if you can see excessive running current before it gets converted to the comp terminals

Sparkletron
02-07-2017, 09:50 AM
The compressor runs for maybe 20 seconds or so, then shut down.
It all seems to happen too quickly to get an accurate measurement of current on the phases.