24-06-2017, 10:49 PM
Hey guys,
This is partially related to my other thread, but since it's a totally different subject I felt it appropriate to start a new discussion to avoid confusion.

What size system would you say this valve belongs on based on Sporlan / Parker's number?

I have a reason for asking, but I want to see what other's come up with on their own.


TEV HCAE 6 KX200 R410.

FaultCode
24-06-2017, 11:34 PM
Looks like 6 TR to me.

The ident is non-standard, it is probably a manufacturers ,Goodman, special code.

MrTube
25-06-2017, 12:58 AM
Looks like 6 TR to me.

The ident is non-standard, it is probably a manufacturers ,Goodman, special code.


Here's the box the replacement from Goodman came in. They sent this based on my serial number.

Mine is a 3 ton system.

Hmmm.

NH3LVR
25-06-2017, 02:47 PM
If you look at the Sporlan website you will see that a 3 ton system will most likely use a different rated valve after you apply the correction factors during the selection process.
A lot of information here
http://sporlanonline.com/literature/10/10-9.pdf

MrTube
26-06-2017, 01:44 PM
If you look at the Sporlan website you will see that a 3 ton system will most likely use a different rated valve after you apply the correction factors during the selection process.
A lot of information here
http://sporlanonline.com/literature/10/10-9.pdf


Thank you for commenting.

I downloaded their sizing tool and it's actually interesting.
Most of the time, they recommend a size 2 TXV for my 3 ton evaporator, especially running in low stage at 2 tons. The size 3 is needed at lower ambient temperatures. A 6, is only needed if running at 3.5 tons and at a fairly low ambient temp but it seems to be grossly oversized for my needs.