PDA

View Full Version : Wiring a sauter actuator



Northy303
24-06-2017, 09:16 AM
I need help wiring an actuator from a controller board that has 3 wires
On the photo wiring diagram it is 25,26 and 27
Thanks in advance14896

FaultCode
24-06-2017, 02:30 PM
Which actuator do you have? Little clues make thing easier :)

Northy303
24-06-2017, 08:27 PM
Which actuator do you have? Little clues make thing easier :)

Sorry mate
It's the adm322sf152
I have 3 wires coming from a rycroft controller board for a hot water heat exchanger they are labelled 25,26 and 27 on the wiring diagram and in the actuator I have mm then 1-6

FaultCode
24-06-2017, 11:43 PM
Is it a 2 port or 3 port valve and do you have any other controls in line with it, i.e. open or close commands.

[Edit] Checking the drawings again I reckon you need scheme 5a but without the feedback loop, so---->

Controller - function - actuator

25 - 2-10v signal - 03
26 - 0 volts - MM
27 - 24 volts - 01

Northy303
26-06-2017, 09:07 PM
Is it a 2 port or 3 port valve and do you have any other controls in line with it, i.e. open or close commands.

[Edit] Checking the drawings again I reckon you need scheme 5a but without the feedback loop, so---->

Controller - function - actuator

25 - 2-10v signal - 03
26 - 0 volts - MM
27 - 24 volts - 01

Many thanks mate
Going there tomorrow so will give it a try
It is just manually fully open at the moment
Will let you know how I get on.

iACS
21-08-2017, 04:01 PM
Should have gone for a Belimo .. :p