Hi friends I want to know reciprocating compressor running with high discharge pressure in plant have air ? and what effects plant when plant in air

mbc
08-06-2017, 07:32 PM
Hi
when you have air in system
your discharge temperature and pressure is high
so your lubrication in compressor is become poor and also you have more pressure and you spend more power and your efficiency comes down .

manmohan
09-06-2017, 12:26 PM
Hi
when you have air in system
your discharge temperature and pressure is high
so your lubrication in compressor is become poor and also you have more pressure and you spend more power and your efficiency comes down .
Thank you MBC my plant discharge pressure is 235 PSI in 30 PSI suction pressure condensing temperature is 34 ' c that is normal ?

mbc
09-06-2017, 05:10 PM
Hi
what is the your refrigerant in the system?

manmohan
10-06-2017, 10:34 AM
Ammonia refrigerant reciprocating compressor 235 tr 6 cylinders 750 rpm

Segei
10-06-2017, 04:54 PM
At condensing temperature of 34C your condensing pressure should be around 180 psig. How did you measure condensing temperature?

RANGER1
10-06-2017, 11:10 PM
Could be a few things need checking

- air in system
- water sprays blocked, poor water distribution, dirty strainers.
- water pump not performing
- build up of scale or calcium on comdenser tubes
- fans not working correctly. direction, air bypass, missing
- condenser to small or mis-matched
- system overcharged with refrigerant, receiver should never be over 80% full


The pressures you have are possibly close to relief valve setting, what are they set to relieve at & what is compressor high pressure switch set to, it should be below relief valves 10 to 15%.

manmohan
14-06-2017, 12:43 PM
Thank you so much