PDA

View Full Version : Carrier Supra 444


ddocwra
18-05-2006, 04:45 PM
Hi,

Can anyone tell me the R404a charge weight for a Carrier Supra 444.

Many Thanks Dave.

Brian_UK
18-05-2006, 05:36 PM
Have you tried the Carrier website, it may be in the manual...
http://search.atomz.com/search/?sp-q=supra+444&sp-a=sp10019d03

ddocwra
18-05-2006, 07:57 PM
Hi Brian,

I checked that out but can only find reference to R12 & R22,Showing a charge weight of 4kgs, Seems high to me.

Thanks Dave

thermo690
19-05-2006, 04:44 PM
Hi,

Can anyone tell me the R404a charge weight for a Carrier Supra 444.

Many Thanks Dave.


Hi Listed below are content of Carriers engineers book


Hope it helps:)
Martin


Supra 444
Refrigerant Type/Charge - kg R404A / 3,2 kg

Diesel Cooling Capacity (-20°c / 0°c) - W 2580w / 4470w

Electric Cooling Capacity -20/0°C - W 2200w / 3590w

Heating Capacity (18/-18°c) - W -

Air Flow - m3/h 1610m3/h

Comp Oil Type EAL 68

Road Comp Type TM16

Displacement - cc 163cc

Capacity - ml 250ml

Stby Comp Type TM16

Displacement - cc1 163cc

Capacity - ml1 250ml

Engine CT2.29TV

Engine Displacement - cc 479cc

Oil Qty (by-pass) - ml 5,2 / 6,1 L

Coolant Capacity - ml 3,3 L

Low / High Speed - rpm 1800 / 2320

WaterT° / Oil Safety Switch - °C 110°C/1 b

Valve Clearance - mm 0,145-0,185

Fuel consup - Liter_High-Low Speed - T ext31°/T int0° 1,56 L

mt frequency Yes

LRA - Amps 64A

MRA - Amps 9,1A

Alternator - Amps 50A

Battery Capacity - Ah 12v / 90Ah

Elec Power Consum at 0°C - W 3800w

Total Consum on Road 12/24 - W No

Total consumption on Stby 230 12/24 - A 15,8

Total Consumption on Stby 380 12/24 - A 9

Setting Air Switch - inch 0,65

Defrost Thermostat Open/Close - °C 9 / 3°C

HP1 - bar 32 / 24

LP - bar - < 0.2

CPR - bar 1,8 b

TXV Orifice 3

Expansion Valve Superheat at 0°C - 6°C

Expansion valve Superheat at -20°C 7°C

Quench Valve Opens/Closes - °C 132°c

CDT - °C No

Overload Relay Settings 230V - 7 Amps

Overload Relay Settings 380V - 6 Amps ¤

ddocwra
19-05-2006, 06:02 PM
Thanks Martin, Thats a Great help.

Dave.