View Full Version : Daikin vrv control wiring



Jase
17-05-2006, 10:08 PM
(a) Approx 8 outdoor units.
(b) Approx 98 indoor units.

Would it be possible to daisy chain all indoor units e.g starting from top floor all the way down to the bottom floor and also link the outdoor units?
There will be no central control used on the project. All units will be individually controlled.
I have a feeling that I will have to daisy chain the vrv's individually, which will be unfortunate!

regards
Jase

puddleboy3
18-05-2006, 12:12 PM
Jase each systems indoor fan coils F1 & F2 wiring have to be kept seperate. Even when not using a Centralised controller i would still recommend connecting the F1 & F2 outdoor connections on your eight outdoors this will enable the sequential start. If you need any more help just let us know the model numbers of your units:)

Jase
18-05-2006, 07:23 PM
Cheers for the advice puddleboy!:)

pasausang
22-03-2011, 05:03 AM
Hello puddleboy3

send to me type:PC9316


Thanks & Regards

JoeAT50A
23-03-2011, 05:01 AM
Hi Jase,
There is impossible to daisy chain all indoor units, should be system by system seperately as puddleboy said.
If not over capacities error, spec are 130% or 200% option for cooling only unit and 150% for heatpump.
Daikin never locked and prompted as capactiy error unlike others.
However please seperate.