View Full Version : Carrier Vector 1550
seanf
23-03-2017, 08:33 PM
Anyone familiar with the Vector 1550 with the scroll compressor and economiser. Only had a brief look at a running unit and though it was strange to see the liquid line being cooled low enough to give it frost after the heat exchanger. +5C ambient, -18C box temp.
Thanks
redroge
24-03-2017, 04:25 PM
Had a liquid line frosting years ago due to the suction crushing the the liquid line in the heat exchanger
seanf
24-03-2017, 07:16 PM
Thanks redroge. Im guessing when the economiser is in play it only drops the liquid temp maybe 5-10 degrees when working correctly.