PDA

View Full Version : Frick RWB II Coalescing filter



WYLBEK
14-03-2017, 01:37 AM
How much oil will be needed when replacing Coalescing filter on a RWB II 60.
Thanks

RANGER1
14-03-2017, 08:10 AM
http://www.johnsoncontrols.com/-/media/jci/be/united-states/refrigeration/industrial-refrigeration/rwf-ii-frick/files/be_spec_frick_rwf_ii.pdf

Page 7 & 27 may be of use.
See torque setting on coalescer filter but on 27

RANGER1
14-03-2017, 09:02 PM
WYLBEK,
From what I can gather 25 gallons oil separator & 3.5 oil cooler.

WYLBEK
16-03-2017, 04:49 AM
Thanks Ranger1, I looked up in manual that it holds 35 gallons in machine, but wasn't sure on how much would be in system elsewhere. 25gallons sounds good to me.

HVACRsaurus
16-03-2017, 05:50 AM
Hey,

Don't forget - the Coalescor is on the weir (dry) side of the separator baffle..

Replacement of the Coalescor should not be impacted by oil in the separator.

Happy tinkering

RANGER1
16-03-2017, 07:48 AM
Hey,

Don't forget - the Coalescor is on the weir (dry) side of the separator baffle..

Replacement of the Coalescor should not be impacted by oil in the separator.

Happy tinkering

Normally we would just change coalescer, Frick recommend change oil as well, because it is a fine filter I guess they want the best for new filters.