View Full Version : to the reefer pros.



jamcool
16-05-2006, 02:07 AM
Have a container unit,no specks at this time but just a question:) ,have noticed that whenever the unit comes "in-range" or close to the set point the suction solenoid closes and the % on the modulating valve will drop from say 100% to say 68% that i understand:D ,but i thought that with the trottle back of the comp. the amps would drop:rolleyes: but on the digital board that gives amps readings for each leg it would read say 20.2 amps on leg A same on leg C but leg B would read say 3-4 amps shouldn't all legs give low readings,my knowledge on containers are a bit limited :o so any help would be good.The unit is working fine set point is 14 F or about -10 C had some time to kill and was going through the digital display:D

Iankp
17-05-2006, 06:48 PM
Sounds like a faulty current device to me but have you any more info like model /make etc?