View Full Version : Question about centrifugal compressors
A.Mortezania
03-03-2017, 07:05 AM
Dear Friends,
Would you please let me know what is the meaning of this sentence ?
"All refrigeration compressors except centrifugal compressors contain oil"
At centrifugal compressor we do not use oil ?
Sincerely yours.
Brian_UK
03-03-2017, 01:30 PM
Generally the motor is external to the compressor and the shaft bearings are also outside of the refrigerant circuit.
There is a lubrication system but it is <within><correction - outside> the refrigerant circuit.
Download the manual for a Carrier 19XRV chiller and look at the lubrication diagram, it will be helpful.
http://eto.carrier.com/litterature/iom/11989_07_2011_IOM_19XR_LR.pdf
A.Mortezania
04-03-2017, 07:19 PM
Generally the motor is external to the compressor and the shaft bearings are also outside of the refrigerant circuit.
There is a lubrication system but it is within the refrigerant circuit.
Download the manual for a Carrier 19XRV chiller and look at the lubrication diagram, it will be helpful.
http://eto.carrier.com/litterature/iom/11989_07_2011_IOM_19XR_LR.pdf
Thanks a lot Brian_UK.