View Full Version : Refrigerant recovery with no circulating water through chiller



Duty007
10-02-2017, 11:16 PM
Hey Guys
Need to recover refrigerant charge on a water cooled chiller..Pumps can not be turned on to circulate water through the chiller while am recovering
What is the safest way or method to recover refrigerant charge with out freezing up any tubes when recovering refrigerant when there's no water circulating through the chiller.Can the push and pull method be applied to recover?

-Thanks

Magoo
10-02-2017, 11:32 PM
Definitely need pumps running, hot wire water pump contactor with a jumper wire

Duty007
11-02-2017, 12:08 AM
Whole system is winterized..got no water in cooling tower and no means to circulate through cooling coils

al
11-02-2017, 12:23 AM
if there is no water in evaporator then you can recover as normal

mbc
11-02-2017, 06:14 AM
14624

Hi
might this can help you