View Full Version : Low cooling in v500 max10 thermo king unit



vsvstephin
26-01-2017, 02:43 PM
Can anyone tell the reason for the fluctuation of pressure in v500 Thermo king unit. Also cooling is not fast

[Edit - thread moved to correct section]

cadwaladr
27-01-2017, 11:36 AM
What fluctuating are you getting,the unit normally uses r404a,the condensor fan is pressure controlled so it will not run until delivery pressure reaches 250 ish then it stops at approximately 170,are you getting any codes on the display panel? If you hold the set button it will show past alarms which will be for example PO1'PO2 etc