22-01-2017, 06:13 AM
Hello
I need a formula to calculate the Ton refrigerant to cool down some liquid from 22 c to 10 c in a double jacketed tank. The cooling media is water. I need to calculate the chiller capacity needed for this process.
Thanks

chemi-cool
22-01-2017, 02:33 PM
Welcome to the forum Omar.

To be able to calculate' please add a few parameters:
- What is the mass? kg, ton?
- Area of heat exchanging? sq/m.
- insulation? Thickness and material.
- No. of cooling circuits?

The more details you supply [pictures are always helpful] the easiest it will be to help you.

mbc
22-01-2017, 05:11 PM
HI
There is a lot of quition
How much you need cool
With whicth temp you want to rich to that
What is you pump flow rates
What is you tansfar heat area
What is the insulation out of tanks
What is the room temp.

Q=MC(T2-T1)