PDA

View Full Version : Discharge Superheat







Oceanlab
11-01-2017, 03:07 PM
Hi Guys

Your thoughts on this . .

Liquid to liquid chiller on R410a with a Scroll comp

Discharge pressure = 13bar
Discharge Temp = 40c

Discharge SH = 21.3C ??

al
12-01-2017, 12:01 AM
that would be correct calculation, only thing is that your discharge pressure is a bit low, what suction pressure have you and suction superheat?

Oceanlab
12-01-2017, 02:27 PM
Hi al

Suction pressure is at 8 bar, temp is at 9.5c. SH = 5.8??

al
15-01-2017, 11:27 PM
yep, 8b is 3.90c.

Oceanlab
22-01-2017, 08:05 PM
Many thanks al