29-10-2016, 08:04 PM
I was looking at a Italian Chiller on Friday, which had a liquid line sight glass.
The sight Glass is suspended above the Liquid Line.
Which has short 1/4" pipe tails either side of it tapped into the Liquid Line.
Does anyone no why this setup is preferred by some?

Surely being above the Liquid Line can cause a false indication of flow?
Grizzly

NH3LVR
29-10-2016, 08:08 PM
I have seen this done. It was installed in order to use the moisture indicator in the small glass.

chemi-cool
29-10-2016, 08:22 PM
I was looking at a Italian Chiller on Friday, which had a liquid line sight glass.
The sight Glass is suspended above the Liquid Line.
Which has short 1/4" pipe tails either side of it tapped into the Liquid Line.
Does anyone no why this setup is preferred by some?

Surely being above the Liquid Line can cause a false indication of flow?
Grizzly

I do it all the time, it saves space, money and time.
Use it from 3\4 and up.

NH3LVR
29-10-2016, 08:32 PM
Grizzly:
I bow to your knowledge.

Grizzly
29-10-2016, 09:38 PM
Grizzly:
I bow to your knowledge.

You Got me my friend!
I am asking because it got me wondering what was the benefit of this design?
I assume the sight glass would be starved first.
Just hoping someone knows more than me.
Grizzly

The Viking
29-10-2016, 09:49 PM
Dear Mr Bear,

Especially on liquid lines with larger diameters it used to be the norm many moons ago when I still did "proper" refrigeration. It kept the costs down at installation but still gave a fairly good indication of charge and flow, not to mention that the moisture indicator still worked.
Also worth remembering is that when the refrigerant flows through the liquid line any gas bubbles will be suspended in the liquid and not separated at the top of the pipe with liquid flowing at the bottom, this means that a (flowing) sample of the liquid/gas mixture will be fairly representative of what is flowing through the pipe as a whole.

:cool:

NH3LVR
29-10-2016, 09:59 PM
You Got me my friend!
I am asking because it got me wondering what was the benefit of this design?
I assume the sight glass would be starved first.
Just hoping someone knows more than me.
Grizzly
Guess I should have replied to Chemi-cool.
Just age I guess!

monkey spanners
29-10-2016, 10:07 PM
Remember seeing a diagram of how to pipe one in, the smaller pipe should enter the bigger one at 45' and have its end cut off at 45' so as to be parallel to the flow in the main pipe and terminate at the center of the bigger pipe. Only benefit i can see is cheapness unless the liquid line is above the size sight glasses are available for.

Grizzly
29-10-2016, 10:12 PM
Thanks Guys!
A rep point for Viking's concise answer.
Thank you.
And thanks to NH3LVR.
For allowing me to realise that its not just me that gets it wrong sometimes!
Cheers Guys!
Grizzly

Grizzly
30-10-2016, 09:36 AM
Thanks Guys!
A rep point for Viking's concise answer.
Thank you.
And thanks to NH3LVR.
For allowing me to realise that its not just me that gets it wrong sometimes!
Cheers Guys!
Grizzly

Interesting info MS.

I was wondering how the flow was directed through the sight glass.
What you say makes sense.
Thanks.
Grizzly

RANGER1
30-10-2016, 08:45 PM
Grizzly, Example from Sporlan

http://sporlanonline.com/literature/70/70-10.pdf

Grizzly
30-10-2016, 09:01 PM
Hi Ranger
Sadly I cannot yet give you a rep point.
Your link is very interesting as Sporlan show the sight glass in the vertical or on the side of the horizontal liquid line.
Which makes sense to me, however the one which I was looking at on Friday is mounted on the top of the liquid line.
They also state on lines above 2,1/8"!
Not sure what actual size these are.
I wasn't looking at the size. Just the configuration.
14406

Excuse my poor photography the photo is shown on its side.
The liquid line is actually horizontal (Clockwise 90 degrees!)