dear all

i know that cooling towers do not be efficient on humid atmosphere ,,,,but what is the maximum relative humidity we can allow to install cooling tower?
thanks:D

US Iceman
10-05-2006, 02:27 PM
afeef,

The cooling tower capacity quickly reduces as the entering air wet bulb temperature increases. If the entering air relative humidity is 100% then the wet bulb temperature is the same as the dry bulb temperature, so the capacity would be almost zero.

You can derate the tower capacity for higher entering air wet bulb temperatures but this has the effect of increasing the tower cost and size.

When the wet bulb temperature begins to reach 80F (26.6C) the tower sizes, costs, and capacities change very quickly.

US Iceman
10-05-2006, 07:40 PM
afeef,

Here is some additional information that may be helpful to you.

http://www.marleyct.com/catlinks/CTII-1.pdf (168 kb)

There are lot of good technical topics on water cooling towers also at:

http://www.marleyct.com/publications.asp

afeef
11-05-2006, 05:28 AM
thanks us iceman
god bless you

US Iceman
11-05-2006, 02:41 PM
Glad to help afeef. I hope the information is useful.