View Full Version : Mitsubishi concealed SEZ-KA35VA not cooling when door is shut closed.



madmax80
17-07-2016, 02:00 PM
Hi,

We have a power multi system at home. For one of the bedrooms, 12 square meters, we use a SEZ-KA35VA bulkhead, which is located in the corridor's ceiling facing to the room just above the room's door . Above the room door we have a linear diffuser grille used for distributing from its upper part and return air from the bottom part. the blades have a 15 degrees diversion facing downwards.

1. When the door is shut, it seems like the air conditioner stops cooling.
2. It starts to make a foul smell
3. The door is pushed towards the doorpost
4. I'm thinking the pressure in the room is raising.
5. When standing just next to the door from the inside of the room, I can feel the wind on my head.

Generally, it seems like the indoor unit doesnt circulate the air well.
Any ideas what can be causing this? The grille was increased and is huge now.. so I dont think that is the issue.

Brian_UK
17-07-2016, 04:05 PM
Sounds like a return air problem.

You say the the lower section of the grille is for the return air, can you check that air is, in fact, moving through the grille?

madmax80
17-07-2016, 06:55 PM
Thanks Brian.

If I put a toilet paper close to the lower area of the grille you can see it sticks to grille, so I assume the air is moving towards the unit. Does that sound right?

Any chance it's something with the unit itself?
I'm lost.

niceman
17-07-2016, 07:37 PM
The grille you held the paper up to has a removeable, washable filter behind it, you should see 2 lugs on one side of that grille which if you slide to the centre of grille will let the grille fall to you, usually hinged on side opposite the lugs.It is advisable to clean filters regularly. Would advise you to do this with the fan off for your safety.

madmax80
17-07-2016, 07:53 PM
Thanks niceman.
The grille doesnt have a filter. the unit itself has a filter and it is totally clean. The unit's air inlet btw is from the bottom not the back if that helps.

Gary
18-07-2016, 02:28 AM
If I understand you correctly, the supply is in the room while the return is in the corridor. Is that correct? And when you close the door between, the room is pressurized? Kinda like blowing into a bottle, the air has nowhere to go so it stops moving.

madmax80
18-07-2016, 06:25 AM
Thanks Gary.
No, both supply and return air are inside the room and are on the same grille. the grille was split so that its upper part is used for supply and it's lower part is used for return air.

I'm trying to think whether something is clogged or the fans are not spinning fast enough. can that explain things?

madmax80
18-07-2016, 08:30 AM
As soon as I open the service door in the corridor, and leave the room's door open, it works amazing. I can fill that the air is thrown strong forward, whereas when the door is shut, the air just falls close to the door. So the unit is OK, but something in the airflow isn't. I have attached images of the grille.
1419914200

Brian_UK
18-07-2016, 10:27 AM
I would therefore suggest that the return air path from the grille back to the unit is blocked off.

Can you see the grille from the access panel? If not then there is the problem.

madmax80
18-07-2016, 12:14 PM
Yeah, I can see the grille from the access panel, it's not blocked. but the blades have some sort of deflection, by design.

Brian_UK
18-07-2016, 03:15 PM
The plot thickens.......

madmax80
18-07-2016, 03:31 PM
what do you mean?

Brian_UK
18-07-2016, 04:44 PM
what do you mean?
We're running out of easy answers.

The fact that the air flow stops shows that there is a problem with the return air path but sadly we can't see from here.

redroge
18-07-2016, 06:47 PM
There must be a return air grille in the ceiling space !

niceman
18-07-2016, 07:29 PM
You say you can see " blades" between the access panel and the grille, this must be dampers which if partially closed will affect air flow, try opening the blades ie increasing the gap between blades and this should increase your air flow. Best of luck.

madmax80
19-07-2016, 11:47 AM
Thanks. The blades are fixed, no dampers, i cant change it. 14201

Gary
19-07-2016, 12:17 PM
The return is pulling air from somewhere other than the room (corridor, ceiling, etc.). You will need to figure out where and how.

madmax80
19-07-2016, 01:09 PM
Thanks Gary. I verified it and sealed everything it doesnt pull air from outside the room. It doesnt pull air from the room either. further more, when the access panel is shut, the unit barely works - i.e lacks return air.

redroge
19-07-2016, 02:03 PM
Can you take a photo of the indoor unit there does,nt seem to be any ductwork between the unit and grille

madmax80
19-07-2016, 02:52 PM
There's no ductwork between the unit and the grille for the return air. there's one for the supply.

Brian_UK
19-07-2016, 06:00 PM
One thing to check, you said that the air filter is totally clean. I would expect some dirt to have been on the filter element.

Is there any air moving through the filter?
What difference is there with the filter airflow when the room door is open or closed?

still learning
19-07-2016, 07:56 PM
So if it blows out thru the large linier grille. At the top and sucks. Back in thru the bottom.
In the ceiling void the cool air. Could sucked. Back into. The. Unit and stop cooling what I could see of you photo from the hatch , which I take is under the unit shows a drain as well.which. My bring smells back in via. Your return air path.
It's quite hard to see what's going on from your photos.
One of the problems of using a. Ceiling void as a open. Expance to pull return air, is. IMHO .
A problem as you get whatever's in the void .
I have a a ducted in my bedroom roofspace and supply blows in via duct work.
And the return air is pulled thru duct work. To a filter box. With a small hatch to access the filter to clean it .

rnine
19-07-2016, 08:12 PM
It seems that an easy fix would be to fit a vent of some description in the bedroom door. This would equalise any pressure differential issues at minimal cost, and you still retain your privacy with a closed door.

madmax80
20-07-2016, 11:26 AM
Thanks guys.
Experiment I did this morning which seems to solve the issue. 14204 put a carton between the supply and the return air. everything now works. it seems like it was sucking everything it was throwing.
The grille blades today are all facing down.
So it seems like I need a new grille where the blades for the supply are facing straight whereas the blades for the return air should face down.

Good^Man
06-08-2016, 02:45 PM
Glad you have sorted it, but:

"As soon as I open the service door in the corridor, and leave the room's door open, it works amazing."

That is the odd thing.

When you crack the door open is there a flow of air out of the room through the crack, or air entering the room through the crack?

Sounds like some of the air enters the room via the grille and the rest from the corridor,
OR some of the extracted air gets back via the grille and the rest via the corridor.

Might be worth a close look in the bulkhead to see what is going on with the airflow.

Has it always had this problem since new or is it a new installation?
Filter clean?