View Full Version : Daikin 1,2,3



Northy303
14-07-2016, 11:00 PM
Did something stupid today wired up a tank pump live and neutral to an old daikin r407 unit only to find that lead number 2 on this particular unit was the comms and 3 was the neutral I soon worked this out after the u4 came on the controller so sorted it out and the unit ran fine with no issues so cut a long story short I had to leave site without checking the pump.could I of blown anything in the pump by putting the the neutral of the pump in the comms cable?

Northy303
14-07-2016, 11:06 PM
It's an aspen 2ltr tank pump tat helps.

r.bartlett
15-07-2016, 06:01 AM
It's an aspen 2ltr tank pump tat helps.

almost certainly not.

Northy303
15-07-2016, 08:22 PM
almost certainly not.

Sorry that was a typo I fitted an aspen hi lift tank pump and put the neutral in the comms cable I think it is 24v dc and I don't know what it would do to the pump it has a 5amp fuse

install monkey
15-07-2016, 09:43 PM
wouldnt do owt to the pump- but sending mains voltage back down the comms line will blow the 3amp fuse on the outdoor pcb, and occasionally zap the board- old daikin/panasonic 407c kit was 1 live 2 signal 3 neutral- new 410 kit 1 live 2 neutral 3 signal- top tip old daikin siesta early stuff was 6 core interconnect- 1 live 4 neutral- 3 gives a neutral until the pot starts

Deano240
06-08-2016, 12:47 AM
As long as you didn't leave it for hours all your boards will be fine. You would have a u4/uf fault