04-07-2016, 06:44 AM
Hi Guys,

i'm going to install a freezer room on my Central Kitchen.
and the place is under renovation right now.

I need insights here guys, because i dont know wether my Freezer Room Contractor give the right equipments or not

here are the details of my kitchen activity:
Central Kitchen for making Chinese Dough "YouTiao" and "Butterfly Bun"

The Central Kitchen will have these steps:
1.Storing
2.Mixing
3.Storing (Freezer Room)
4.Defrost - ing
5.Frying
6.Packaging or Selling

Here is the floor plan if you want to see (on attachemtn XDL_1st)
so the situation here, the room will be between mixing room and frying room (don't worry the frying room will have decent exhaust and ducting for the air flow).

Here are the items that im going to put on the freezer room:
1.Dough
2.Dough degree around 15-25c
3.Dough expected to be -5 c
4.Cooling down time 1-2 days no problem
5.will be put on a tray (there's hole on the tray on each side) 1 tower of tray approx 158 kg (22 trays)
6.room will be expected on 1st year of production 6000 KG
7. dough will be put one by one.

Here are the specs that my contractor give to me:

1.Insulation Pannel 100mm, plate color bond 0,5 mm inside & outside
2.Density 42 kg / m3
3.2 swing doors
4.flooring - PU panel
5.compressor - Bitzer 3 HP
6.Evaporator Muller
7.Price USD 15.254 exclude tax 10%

so..
others also offer me to use 4hp Copeland Fully hermetic (ZXL040E-TFD) and 5hp COPELAND.

so what do you guys think,
should i use the 3 HP ? because this freezer room will effects to my COGS per product!

chemi-cool
04-07-2016, 02:56 PM
It looks ok, go with your contractor, the bitzer semi hermetic is better.
Make sure your guarantee covers all the problems with the freezing unit and compensation on loss of merchandise .

GudegRice88
06-07-2016, 11:37 AM
It looks ok, go with your contractor, the bitzer semi hermetic is better.
Make sure your guarantee covers all the problems with the freezing unit and compensation on loss of merchandise .

hey thanks for the reply.

so i dont have to use the 4hp or 5hp?

then ill go with the 3 Hp

Magoo
07-07-2016, 03:28 AM
What ever, get a performance gaurentee warranty from installer. I would tend towards larger system as you will hammer any system to death and complain when it does not suit your growing business.

GudegRice88
07-07-2016, 07:27 AM
What ever, get a performance gaurentee warranty from installer. I would tend towards larger system as you will hammer any system to death and complain when it does not suit your growing business.

so you suggesting to take the 4 hp instead of 3?

chemi-cool
07-07-2016, 02:43 PM
so you suggesting to take the 4 hp instead of 3?

Without checking, I believe the 3 hp bitzer will have greater capacity than the 4 and 5 hp hermetics.

Check and compare the capacity of all 3 compressors/