View Full Version : ac unit condensate water
kefah
27-06-2016, 05:26 PM
Hi all
i have question about water condensates from ac unit which drained outside
if AC unit works perfectly
then y sometimes there will be no water drain
or why it will be too much water
what condition that could prevent it or decrease or increase it
Brian_UK
27-06-2016, 08:31 PM
It depends on the ambient humidity level whether there is any excess moisture to be removed from the air.
kefah
27-06-2016, 08:51 PM
outdoor humidity is 19%
temperature is 46 C
The Viking
27-06-2016, 09:49 PM
When it comes to AC and humidity it is the room humidity that counts.
But with ambient being as low as 19% I guess the room humidity would be really low as well.
Generally if you have a room humidity of less than ~30% there will be little or no dehumidification by the evaporator and therefore little or no condensate.
If on the other hand you got a high room humidity there will be vast amounts of condensate.
:cool:
Tayters
27-06-2016, 10:22 PM
Hi Kefah,
Glad to see you are keeping well.
Stay safe,
Andy.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.