22-06-2016, 05:30 PM
First time on here so be gentle

Have a Carrier Chiller RA 30

Comes up with an Error 34 fault as far as I can work out, this is a reverse rotation fault thrown up by sensors not picking up a difference in pressures.

The compressor does not even try to start just goes in to fault

Sensors on Pro Dialog are reading correctly and do change readings when compressor is helped to run

Checked Hp switch this is made , checked connections to the board all correct

Anyone have any ideas or is it time to call in a man with a laptop

Thanks

Gibbo
23-06-2016, 11:55 AM
The fault is the compressor not starting. Check to see if there is a compressor protection module such as a Kriwan module contact / overload contact which could be preventing the compressor starting.
Gibbo

Blata
23-06-2016, 07:58 PM
Thanks for that, the compressor is not pulling in, overload is good and that is the only protective device.
Must be the board not giving an output signal

Thanks