PDA

View Full Version : Refrigerant R502



kkchiew
06-05-2006, 06:48 PM
Dear All

Hi, good day to everybody.
I m studying the refrigeration system.

I had extracted the p-h chart for R502 from the coolpack program.

Could any one confirm that the chart is correct, as i found one in my book is different from this.

thanks for your help.

Peter_1
06-05-2006, 09:22 PM
What's exactly the difference?
Are the units the same?;)

US Iceman
06-05-2006, 10:20 PM
The difference may be due to the zero enthalpy point on the diagrams. This does not make any difference in the calculations as long as you only use one diagram.

Do not mix values from one diagram to another as you will end up with incorrect answers.

Josip
07-05-2006, 08:41 PM
Hi Kkchiew,

You should sent the jpg from your book not from CoolPack, becuse all of us have that program but that book only you have ;)

How we can check the difference :confused:

Best regards,

Josip :)