26-05-2016, 07:57 PM
I could some kind person help me please, I have a Mitsubishi puhz-rp125yha2.
The suction pipe is frozen all the way into the compressor. I have check filters, fan motors and coils. All ok. Is this liquid coming back to the compressor or possible charge issue?

Thanks

Deano240
26-05-2016, 09:15 PM
Check the expansion valve isn't fully opened

Craig Johnston
27-05-2016, 07:33 AM
How do you check that with the lev? Thanks

Craig Johnston
30-05-2016, 09:27 AM
No errors. Unit is working ok

install monkey
30-05-2016, 08:42 PM
is this the pipework within the condenser or the suction line from evap to condenser- is the lagging 13mm wall? you can get away with 9mm but if lagging is compressed with cableties or squashed on cable tray then that can cause sweating/frosting on suction line?- run it in test mode and view coil temp should be above freezing- otherwise ****ted up coil?

Craig Johnston
30-05-2016, 09:04 PM
Thanks guys much appreciated for the advice.

frank
01-06-2016, 06:50 PM
Are the indoor filters clean?