r.bartlett
16-04-2016, 04:23 PM
Chaps,

looking at a Haier ducted split which has been playing up for some time. The previous company diagnosed a faulty compressor but on running it seems fine although the unit stops after a minute of operation on either heating or cooling

There is a hard wired controller but no faults show. The indoor board has flashing lights but seem more random.

One thing I did notice that the outdoor ambient sensor had been chopped and the wired taped together, the actual sensor was missing

I assume the first thing would be to replace the sensor but wonder if anyone has any ideas?

Richard

install monkey
16-04-2016, 08:09 PM
when it stops is it comp only or cond fan? - might be worth sticking a resitance box or a fixed resistor to trick it to think the ambient is 28deg- which it prob is in your hood, would have thought that the system wouldnt run at all if senssor is linked out

install monkey
16-04-2016, 08:10 PM
condensate hi limit float switch?

Tayters
16-04-2016, 09:22 PM
Found this install manual if of any use, has some fault code info:

http://www.google.co.uk/url?sa=t&rct=j&q=&esrc=s&source=web&cd=3&cad=rja&uact=8&ved=0ahUKEwi3nLP2-ZPMAhXMWBoKHYZWDQQQFgg2MAI&url=http%3A%2F%2Fwww.haiercondizionatori.it%2Fdownload.aspx%3Ffile%3D7923_AD12-18MS1ERA-UM.pdf%26al_id%3D7923&usg=AFQjCNFohbqNs6MrK82Spjvia7ifMPcnBw

and another one here which I'm not sure applies to your model but has all sorts of service info inc. probe resistances:
http://www.google.co.uk/url?sa=t&rct=j&q=&esrc=s&source=web&cd=1&cad=rja&uact=8&ved=0ahUKEwizrKDs-5PMAhWEJhoKHY_rB0cQFggjMAA&url=http%3A%2F%2Fimage.haier.com%2Fmanual%2FAirconditioner%2F201108%2FP020110831595246434785.pdf&usg=AFQjCNEcUUr77Lsn5PDYuZwsYp9tyPIsIA

Other than that not really messed about with Haier.

Heard someone describe them as worse than LG if you could confirm? :-)

Cheers,
Andy.

r.bartlett
17-04-2016, 09:17 AM
Thanks chaps, no fault codes just runs for one minute off 5 ..

frank
17-04-2016, 07:54 PM
Don't suppose it's clever enough to consider frost protection on the evap?

r.bartlett
17-04-2016, 09:21 PM
Don't suppose it's clever enough to consider frost protection on the evap?

It was 25 deg C so unlikely but it was to the second which means the pcb was timing an error but not reporting it.....:-)