PDA

View Full Version : Eurofrigo c3500







xipodil
28-03-2016, 10:18 AM
Does anyone have wiring diagram?
Best regart.

cadwaladr
28-03-2016, 05:07 PM
Sorry I don't have one,but they are quite simple, relays cut out switched for high and low pressure a pressure switch to activate the condensor fan the controller is a dixell the model number is on the back of it,are you having problems with it,I have quite a few units that I look after and never had problems with the need for a diagram.

xipodil
28-03-2016, 06:28 PM
Controller is Microstat 14050 which, communicate with some buffer board 14051 . That buffer board is broken. I want to replace the controller Microstat, with controller Dixell or similar. Which one I want to connect directly to Relay Board 14052. So I want to know does the Relay board have internal interlocks between sensors and relays?

cadwaladr
28-03-2016, 08:35 PM
You will need to rewire from the cab to unit with stronger wire,elliwell 974 12volts and rewiring at the unit,big job.

xipodil
29-03-2016, 08:28 AM
Rewiring is not problem. More difficult is to tracking wire between sensors, fans, etc and relay board. I wanted to keep relay board, but when is not possible I must replace it with a lot of relay. With wiring diagram is more easier.

cadwaladr
30-03-2016, 12:13 AM
There's an old mate comes on here sometimes he will have a diagram,but not seen a post from him in a long time,maybe he won the lottery or retired to the Welsh valleys!