08-03-2016, 01:26 AM
Hi All,
Long time reader of the forum, first time poster!
We have an issue with a cool room on site where meat is being stored. The room is served by a single condensing unit, located outside and single evaporator. The room is being maintained at 2deg C and currently runs around 90-95% humidity.
This is creating problems and the site would like to see humidity levels brought back to 80-85%. The room is accessed quite frequently and it is difficult to keep the doors closed for significant period of time. Curtain strips have been installed to reduce the infiltration load, but the room is still prone to high humidity.
I am going to visit site soon to get some more details, but am thinking the evaporator may be over-sized, enabling the unit to operate at low TD and reducing dehumidification.
I want to get an idea about the pressure control setup of the compressor and how often the unit cycles on/off. The client is keen to try to make the existing setup work before doing any equipment changes.
Some ideas I have currently:
- Change pressure controls (increase differential pressure setting) so that unit cuts out at lower pressure/temperature, runs longer and provides more dehumidification.
- Blank off a part of the evaporator air inlet to reduce heat transfer area of the evaporator and achieve a higher TD.
Any thoughts on this? Anyone who's seen similar issues and tried solutions? What would be a typical design TD (I know rule of thumbs can't be relied on, but would be good to get an idea) for a system like this?
Thanks a lot!
Long time reader of the forum, first time poster!
We have an issue with a cool room on site where meat is being stored. The room is served by a single condensing unit, located outside and single evaporator. The room is being maintained at 2deg C and currently runs around 90-95% humidity.
This is creating problems and the site would like to see humidity levels brought back to 80-85%. The room is accessed quite frequently and it is difficult to keep the doors closed for significant period of time. Curtain strips have been installed to reduce the infiltration load, but the room is still prone to high humidity.
I am going to visit site soon to get some more details, but am thinking the evaporator may be over-sized, enabling the unit to operate at low TD and reducing dehumidification.
I want to get an idea about the pressure control setup of the compressor and how often the unit cycles on/off. The client is keen to try to make the existing setup work before doing any equipment changes.
Some ideas I have currently:
- Change pressure controls (increase differential pressure setting) so that unit cuts out at lower pressure/temperature, runs longer and provides more dehumidification.
- Blank off a part of the evaporator air inlet to reduce heat transfer area of the evaporator and achieve a higher TD.
Any thoughts on this? Anyone who's seen similar issues and tried solutions? What would be a typical design TD (I know rule of thumbs can't be relied on, but would be good to get an idea) for a system like this?
Thanks a lot!