I just install a new pc board to this condensing unit and it just wont work error code is UA can someone assist

monkey spanners
21-02-2016, 07:34 PM
https://www.climatecenter.co.uk/wcsstore/ClimateCenter/Attachment/downloads/daikin-trouble.pdf

Looks like there are some dip switches or similar that need setting for it to work, its wired wrong, or its the wrong board.

install monkey
21-02-2016, 09:43 PM
why was the board changed?- what was the original fault?
some daikin pcbs req a capacity setplug that tells the pcb the size of the outdoor unit