Octopush Technology Controller 8320-220V Parameter List


Grup

Sıra



Parametre


Birim
Min
Max

Default






Fan


1


frc


Y/N


No


Yes


No
Fans on with the compressor





2


fst


C


-55


110


15
Fans stop upper limit





3


Fdf


C


0.1


10.0


3.0
Fans differential





Cpr


4


Cdf


C


0.1


10.0


3.0
Differential





5


Scd


min


0


10


1
Compressor delay after start up





6


Sad


min


0


10


1
Delay for compressor switch on





7


Hst


C


-55


110


15
Maximun allovable temperature





8


Lst


C


-55


110


-10
Minimun allovable temperature















Dfr


9


Dft


C


0


100


25
Defrost end temperature





10


Ddu


min


1


60


35
Maximum defrost time





11


Dt


NDF / HG / AIR / EL


0


3


3
Defrost type :0: No defrost /1: Hot gas/2 Off cycle/ 3:Heater elements





12


Sdd


hr


0


24


1
Defrost delay on start up 0: Defrost cancelled





13


Dit


h


1


24


6
Defrost interval.





14


Dct


Ct/Rt


0


1


1
Defrost interval/: 0: Compressor on time /1: Real time





15


Drt


min


1


10


10
Drip time after defrost





Alr


16


Hrt


C


1


10


3
High temperature alarm





17


Rtd


min


1


240


30
High temperature alarm delay





18


Lrt


C


1


10


-3
Low temperature alarm





19


Ad


min


1


240


180
Alarm delay at start up





20


Dad


min


1


240


60
Alarm delay after defrost



Cfg



21


Set


C


Lst


Hst


-5
Set temperature.





22


Tpc


C


-12.8


12.8


0
Room sensor calibration





23


Epc


C


-12.8


12.8


0
Evaparator sensor calibration





24


Out


Vers


0


0


20
Octopush Version





25


Adr


Adres


0


254


1
RS485 com address





Dsp


26


Tsd


0/0,0


No


Yes


Yes
Display resolution: Integer / Decimal





27


Dts


def/set/t


0


2


0
Display during defrost: Def / Set valuei / Room temperature





28


Ptd


t/e/c


0


2


0
Temperature displayed: Room / Evaporaor / Condenser