Hey gus i wonder if can find grasso screw compressor type 400GL service manual. It will be great if anyone can help me get it. Because i really need it


Best wishes

cricri
03-02-2016, 07:50 PM
Nearly impossible to help you seleem,
I don't know this reference.
Actualy it could be a letter and a number, S2 for exemple.
In years 1990 it was 3 letters and 2 or 3 numbers ie GSL 185. Grasso Screw Large and swept volume at 2950rpm / 10.
Then, depending if it is the beginning of 1990 or the end, it could be a Sullair made or a Howden made.
Is it possible to get a pict of the name plate?

RANGER1
03-02-2016, 10:08 PM
Looks like LT-V from this.

http://www.cbarrantes.com/documents_archivos/Cross_Reference-Open_Screw_Compr-Bitzer_and_FES_Vs_Howden_and_Kobe-R.1.pdf

cricri
04-02-2016, 06:31 AM
you are right Ranger
400GL is a FES design for a V compressor,

cricri
04-02-2016, 10:23 AM
Seleem, check your Email

cricri
10-02-2016, 10:58 AM
Seleem, it's free, you can say thank you!

seleem
10-02-2016, 06:17 PM
Thank you very much sorry i was busy the last few days

seleem
10-02-2016, 06:21 PM
I checked the the compressor unit and the 400gl is the compressor package name and you are right it ia fes package

seleem
10-02-2016, 06:42 PM
Hey man i just now downloaded the you sent me it so helpful.