View Full Version : PURY-P250YGM-A 1102 fault



spamfish
17-12-2015, 08:58 AM
1102 fault driving me mental

PURY-P250YGM-A
Indoor units gutted and clean until they shine
Outdoor unit gutted and cleaned
correct gas charge in unit
1102 now appears and then 1302
compressor going to 112 deg c then ramps down to 75 deg c then up to 112 again (heating)

any advice?

Rob White
17-12-2015, 12:35 PM
1102 fault driving me mental

PURY-P250YGM-A
Indoor units gutted and clean until they shine
Outdoor unit gutted and cleaned
correct gas charge in unit
1102 now appears and then 1302
compressor going to 112 deg c then ramps down to 75 deg c then up to 112 again (heating)

any advice?


Don't Gut and Clean em...................

:D

Rob

.

Lastguest
21-12-2015, 01:52 PM
Check inddor fileter n non condensibles

frank
21-12-2015, 03:44 PM
The compressor is going into protection mode due to the high discharge temp. It's a typical sign of overheating and if you don't address it you will lose the compressor.

I would check the oil level in the compressor with an infra red thermometer. If it's low then add a little oil into the suction line

Deano240
21-12-2015, 09:07 PM
Is this in heating mode? I would check LEV 3 in the BC box. undo it to see if it's stuck