I have problem with Climaveneta chiller/heat pump and the controller

The machine use Water 300 controller .

And now shows :
AL:003 – Evaporator pump thermal protection

After i reset the alarm manually it shows it again and again .

Any idea what to do ?

redroge
25-11-2015, 02:40 PM
Check pump motor and contactor reset overload check running amps

chemi-cool
25-11-2015, 04:30 PM
Could be a thermistor in the pump motor winding.

See if there extra 2 wires in the motor connection box.