View Full Version : Need help installing a new a/c system
attila07
05-07-2015, 08:41 AM
Hi . I have too install a new A/C system and between the outdoor unit and the building it's a side walk and I have to go with the piping (7/8 inch) underground for 6 feet .`
My question is if I have too put a trap for the oil ? I am 95% sure that I have too , but it's better to have others opinion too .
Thanks
13802
nike123
05-07-2015, 09:18 AM
You don't need to put trap. Speed and density of refrigerant is enough to return oil, and inverters have function to recover oil in prolonged operation on low revolutions.
CONROD
05-07-2015, 08:41 PM
Check the manufacturers installation manual. On some units you have trap every 10m if the outdoor unit is below the indoor as your diagram shows.
r.bartlett
05-07-2015, 11:09 PM
Hi. I got a AHAM-NARDA refrigerant recovery certificate in USA from 2006. Does anyone know if that is recognized her in the UK? THANKS
Did you get your f-gas btw?
The Viking
06-07-2015, 02:00 AM
Always follow the installation manual, always.
As you haven't said what kit you are installing, nobody will be able to give you the "right" advice but the install manual that comes with the kit will always be right.
:cool:
attila07
06-07-2015, 11:45 AM
Hi. Thanks for answers. The outdoor unit it is a Daikin rzq250. In the installation manual says install trap at each difference in height of 10 m. I have only 3 m in height difference
frank
07-07-2015, 09:04 PM
Hi. Thanks for answers. The outdoor unit it is a Daikin rzq250. In the installation manual says install trap at each difference in height of 10 m. I have only 3 m in height difference
Then you do not need an oil trap