View Full Version : Serious problem with Chiller Carrier 23XRV



bk2012
25-06-2015, 11:24 AM
Dear all,
- Fault state is 220: Ground Fault Trip; Check Motor and Current Sensors
- 2 minutes later, error appears 223 :Ground Fault Trip; Check Motor and Current Sensors
I checked GROUND FAULT CURRENT andVFD FAULT CODE in VFD_HIST screen , the fault code is 216.
When this error appear, I can't reset on ICVC display. I have to off power supply to Chiller, error reset
I measured grounded input wiring and insulation cable is OK
This is the 3rd time I encountered this error.
Can you give me any advice?
Best regards!
Thank you so much!

goshen
03-07-2015, 12:54 PM
Hi
check your cabling ,since you are using a vsd,the cabling must be low capacitance shielded cabling .

good luck

bk2012
10-07-2015, 07:45 AM
Hi
check your cabling ,since you are using a vsd,the cabling must be low capacitance shielded cabling .

good luck
Thank for your answer!
I used megaohm check cabling. I stiil not see anything unusual,:(
Best regard!