chiller Lennox LCH803
How to disable the operation of the compressor 1,2
Controller CLIMATIC 50
In the work leave the compressor 3
Thank you for your support

Martin Davies
20-06-2015, 06:58 PM
Surely they have there own breakers?

Freon959
20-06-2015, 07:11 PM
disable by modifying the parameters of the program

Martin Davies
20-06-2015, 07:50 PM
Do you mind if I ask why?

See free contacts;

13790

Freon959
21-06-2015, 09:57 AM
Martin
Thank you for contact (free) information

Grizzly
21-06-2015, 12:14 PM
Hi *****959.
Following on from Martin's post.

I cannot confirm these settings will work with your 3 compressor model LCH.
But 3411 is for comp 1 and 3412 is for comp 2 on some models. Once entered you should be able to switch the relevant comp on or off!
Grizzly

Freon959
21-06-2015, 01:57 PM
Hi Grizzly
it's clear
Setting(code 3000)>1.General
2.Schedule
3.Control
4.Compressr (code 3400)> 1.Circuit (cod3410) > 1 Rotat.(cod3410)>3411
>3412
Thank you

Freon959
21-06-2015, 02:00 PM
correction
1 Rotat.>3411
>3412
Thank you

Freon959
24-06-2015, 06:01 PM
Hi Grizzly
right
4.Compressr (code 3400)> 1.Circuit (cod3410) > 1 Enable.(cod3411)
choose from ready-made
С1--
С-2-
С1.2-
С--3
С1-3
С-2.3
С1.2.3. Thank you