PDA

View Full Version : Chiller YORK YCIV0840 Baseplate



Freon959
06-06-2015, 05:58 AM
Hello all
chiller York YSIV0840
Faulty pump glycol
The display shows: SUS1 LOCKOUT : HIGH VSD BASEPLATE TEMP.
Please, provide technical support and help
Sincerely, Anatoly

Freon959
06-06-2015, 06:08 AM
amendment YCIV0840SA50VAB

hookster
06-06-2015, 06:56 AM
Hi Anatoly
Is your glycol pump ok? Check glycol level.
Check the cabinet fan or you may have a faulty sensor

Freon959
06-06-2015, 10:00 AM
Hi hookster
The pump is faulty.
It was the starting block with a broken pump.
Tell me where the sensor?
What are the terminals connected?
Do I need to manually reset this accident?

moideen
06-06-2015, 01:10 PM
Hi hookster
The pump is faulty.
It was the starting block with a broken pump.
Tell me where the sensor?
What are the terminals connected?
Do I need to manually reset this accident?
you said already the glycol pump is faulty.i dnt know what type of pump fault. repair or replace it.

Freon959
06-06-2015, 03:40 PM
The pump is already engaged may replace a new one
problem
Display Indication Sus1 BLOCK: HIGH TEMPERATURE IRR baseplate.
Removing the accident and where the temperature sensor

Freon959
06-06-2015, 03:41 PM
amendment SUS1 LOCKOUT : HIGH VSD BASEPLATE TEMP.

moideen
06-06-2015, 06:30 PM
"Removing the accident"cannot understand. what is the glycol level? if glycol level is low, base plate temp will go high.

Freon959
06-06-2015, 08:29 PM
circuit status off
where the temperature sensor is installed

nuwanchamara
20-09-2015, 09:49 PM
Leave sensor location it is on PCB you can not do anything...... If u replaced Glycol pump just topup glycol.......untill overflow then close cap.