View Full Version : minimum length pipe run between indoor and outdoor on mitsubishi heavy industry



sork
20-05-2015, 07:14 AM
Hi guys , installing a split mitsubishi heavy industry , outdoor unit FDT140VF , indoor unit cassette FDC140VN, what is the minimum pipe length between indoor and outdoor unit? may need to recover some refrigerant out of the system.

Brian_UK
20-05-2015, 10:41 PM
Can't see anything written down in their tech manual....
http://www.manualslib.com/manual/850996/Mitsubishi-Heavy-Industries-Fdt-Series.html?page=149#manual

sork
22-05-2015, 10:20 PM
with some units the short pipe run causes water droplets from the evap surface ; if you retired you may not need to know the manufactures brand, if you think the liquid remains in the liquid receiver or the condenser, with certain units that does not comply, what i ment was the distance to be less than 2m.
thanks for the reply????????????????

install monkey
23-05-2015, 08:51 AM
only small splits under 5kw highlight a minimum of 1.5mtr run- shouldnt matter on a mhi as the lev will control the superheat , best practice is to RTFM;)