View Full Version : Fujitsu split air conditioner unit Low side valve



Bagel
30-04-2015, 07:21 PM
I have a new Fujitsu split unit. It was low on the refrigerant. When I'm trying to remove the gauge I'm getting a strong refrigerant pressure. The low side valve is in shut position. It turned all the way off. Now I can't remove the gauge. Do you think I have defective low side valve.

install monkey
30-04-2015, 08:26 PM
low side valve should be open! once installed an comissioned

Bagel
30-04-2015, 08:43 PM
I really appreciate if you could give me some guideline. I assume I have defective nipple. But I don't know how to replace it. I have lots of pressure there. The refrigerant is 410A. As soon as I loosen the gauge hose adapter the refrigerant starts coming out under high pressure. If I still remove the hose adapter I'm running out of refrigerant.
Thanks,

Brian_UK
30-04-2015, 09:10 PM
There will always be pressure at the Schrader valve.

Use a quick connector in future.

What qualifications do you have to work on refrigerants?

Bagel
30-04-2015, 09:15 PM
Thanks for the reply. I'm EPA Universal Certified. We repair commercial refrigeration appliances and commercial bakery equipment.

martinw58
01-05-2015, 06:32 AM
with the valve closed the Schrader is open to the system close the valve on the expansion (liquid) line and pump the unit down to remove your gauge