Hi guys.
Maybe some of you has wiring diagram for YAES 0595 SB? Can't sort out inputs for flow switch and circuits remote on-off.
Cheers

al
13-03-2015, 06:13 PM
i've no wiring diagram, this is from install manual,any good?


Flow Switch
A chilled liquid flow switch of suitable type must be
connected to terminals 13 and 18 to provide adequate
protection against loss of liquid flow.
Remote Start/Stop
Remote start/stop can be accomplished using a time
clock, manual contact or other ‘voltage free’ contact,
terminals 15 and 18 with terminals 12 and 15 linked in
the control section of the control panel. The contact
must be closed to allow the unit to run. Any time the
contact opens, the unit will shutdown and the ‘NO RUN
PERM’ message will be displayed.
For individual system start/stop contacts connect No. 1
system to terminals 15 and 18 and No. 2 system to
terminals 12 and 15. With the associated contact open
the ‘NO RUN PERM’ message will be displayed and the
associated systems will not run.

install monkey
13-03-2015, 11:11 PM
https://drive.google.com/file/d/0Bz6TBzB0zKeAZ2pWV1RvWmlqSlE/view?usp=sharing
page 35

AlexG
14-03-2015, 01:19 PM
Thank you guys.