24-04-2006, 09:36 AM
HI Sirs
Pls give your ideas:)
Need to select a TEV for a R22 system of capacity 56KW(16USRT)at Te=10C ,Tc=48C. I choose Emerson Alco TEV HFE valves(nominal 15USRT),it's a litter higher than norminal at this condition.
It's a parellel compressor system,while single compressor is working. The capacity is 50% of full load.
If the TEV adapt to the change,the mass flow across the valve decrease and the pressure drop should become small,then the evaporative pressure and condenser pressure difference should be small.
I wonder if there's minimum pressure diff requirement across the valve. if so, can the TEV properly work at 50% loading situation:confused:
regards
LC
Pls give your ideas:)
Need to select a TEV for a R22 system of capacity 56KW(16USRT)at Te=10C ,Tc=48C. I choose Emerson Alco TEV HFE valves(nominal 15USRT),it's a litter higher than norminal at this condition.
It's a parellel compressor system,while single compressor is working. The capacity is 50% of full load.
If the TEV adapt to the change,the mass flow across the valve decrease and the pressure drop should become small,then the evaporative pressure and condenser pressure difference should be small.
I wonder if there's minimum pressure diff requirement across the valve. if so, can the TEV properly work at 50% loading situation:confused:
regards
LC